Worcester boiler issues ....

  • 28-02-2018 5:29pm
    #1
    Registered Users, Registered Users 2 Posts: 2,573 ✭✭✭


    My condenser boiler has some issues. I had it installed 2 years ago and had a power flush done prior to install. I notice my rads don't get as hot as other houses I've been in. I had the heat exchanger changed out last year due to over temp issues. It was initially set to max but even after the heat exchanger was changed I had to ramp the temp down to 75 to prevent temp errors. I checked the copper pipe supplying heat to my system the at the bottom of my boiler and it's only reading 55 degrees on my meter even though it's 75 on the boiler display. What temp should it be? Any ideas folks?


Comments

  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    Assume its still under manufacturers warranty.


  • Registered Users, Registered Users 2 Posts: 2,573 ✭✭✭Fingers Mcginty


    DGOBS wrote: »
    Assume its still under manufacturers warranty.

    Yes it is


  • Registered Users, Registered Users 2 Posts: 2,573 ✭✭✭Fingers Mcginty


    would people mind ;if you have the means; to check the temp of the pipe from the boiler feeding your rads. Mine is at 55 degrees even though the boiler is set to max. I have my cylinder stat set to 65 degrees so how will my hot water ever reach 65 if the temp of the water flowing through the coil is only 55?


  • Moderators, Home & Garden Moderators Posts: 6,380 Mod ✭✭✭✭Wearb


    would people mind ;if you have the means; to check the temp of the pipe from the boiler feeding your rads. Mine is at 55 degrees even though the boiler is set to max. I have my cylinder stat set to 65 degrees so how will my hot water ever reach 65 if the temp of the water flowing through the coil is only 55?

    It wont. It can only reach 55C

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 2,573 ✭✭✭Fingers Mcginty


    exactly....that's what i was thinking. Must be an issue with the boiler?
    Heat ex was changed out this time last year.


  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,380 Mod ✭✭✭✭Wearb


    exactly....that's what i was thinking. Must be an issue with the boiler?
    Heat ex was changed out this time last year.

    I am assuming that the cylinder doesn’t have a separate feed from the boiler and a different feed for the heating. If they both have seperate feeds, then they both might be able to run at different temperatures. I am not familiar with gas boilers so I can’t answer with any certainty.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 2,573 ✭✭✭Fingers Mcginty


    Wearb wrote: »
    I am assuming that the cylinder doesn’t have a separate feed from the boiler and a different feed for the heating. If they both have seperate feeds, then they both might be able to run at different temperatures. I am not familiar with gas boilers so I can’t answer with any certainty.

    No.... same feed


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    So if your boiler stat is set to max, your flow pipe (the hotter of the 2) only reads 55?


  • Registered Users, Registered Users 2 Posts: 2,573 ✭✭✭Fingers Mcginty


    Yes the flow pipe only gets to 55 when the boiler is set to 80 degrees celcius.
    When i set it to 65 I'm only getting 45 degrees on the flow pipe.


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Yes the flow pipe only gets to 55 when the boiler is set to 80 degrees celcius.
    When i set it to 65 I'm only getting 45 degrees on the flow pipe.

    How many rads do you have and what kw size is the boiler?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,257 ✭✭✭Pete67


    Are you certain you are measuring the temperature on the flow and not the return?


  • Registered Users, Registered Users 2 Posts: 2,573 ✭✭✭Fingers Mcginty


    Dtp1979 wrote: »
    How many rads do you have and what kw size is the boiler?

    4 bed detached house with 11 rads
    bosch worcester greenstar 24i


  • Registered Users, Registered Users 2 Posts: 2,573 ✭✭✭Fingers Mcginty


    Pete67 wrote: »
    Are you certain you are measuring the temperature on the flow and not the return?

    Yes definitely the flow pipe i'm measuring.
    The return has a magnaclean so i know which is which :)


  • Moderators, Home & Garden Moderators Posts: 6,380 Mod ✭✭✭✭Wearb


    Yes definitely the flow pipe i'm measuring.
    The return has a magnaclean so i know which is which :)
    What's the temp on the return?

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 2,573 ✭✭✭Fingers Mcginty


    Wearb wrote: »
    What's the temp on the return?

    10 degrees lower than the feed pipe


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    10 degrees lower than the feed pipe

    That’s a strange one to be honest.
    Turn off all radiators and only heat the cylinder. Does the pipes heat fully then?
    Other than that I’m wondering if the boiler kw output is turned wayyyy down in the settings perhaps.


  • Moderators, Home & Garden Moderators Posts: 6,380 Mod ✭✭✭✭Wearb


    Have you added any rads recently? Or had the boiler derated?

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 2,573 ✭✭✭Fingers Mcginty


    It's the same when I'm just heating the coil in the cylinder.
    I'm thinking that it is actually hitting 80 degrees in the boiler itself as it has gone over temp a few times and i had to reset it and turn the temp down to 75.


  • Registered Users, Registered Users 2 Posts: 2,573 ✭✭✭Fingers Mcginty


    Wearb wrote: »
    Have you added any rads recently? Or had the boiler derated?

    No


  • Moderators, Home & Garden Moderators Posts: 6,380 Mod ✭✭✭✭Wearb


    Have you tried another measuring instrument?

    Please follow site and charter rules. "Resistance is futile"



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,573 ✭✭✭Fingers Mcginty


    Wearb wrote: »
    Have you tried another measuring instrument?

    Yes I've used a fluke infra red on the supply and return lines and they tally up with my initial readings from my other meter.


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    It's the same when I'm just heating the coil in the cylinder.
    I'm thinking that it is actually hitting 80 degrees in the boiler itself as it has gone over temp a few times and i had to reset it and turn the temp down to 75.

    If the boiler is getting to 80 in the heat exchanger or is overheating then the flow pipe will be at that temp. It just won’t reach the rads. I wonder if somebody turned down the kw output when your first heat exchanger was acting up?

    Edit. I assume you’re giving the boiler a couple of hours to heat up because some WB boilers have a function on start up that the boiler fires for 15/20 mins and dosent go above 45 degrees.


  • Registered Users, Registered Users 2 Posts: 2,573 ✭✭✭Fingers Mcginty


    Dtp1979 wrote: »
    If the boiler is getting to 80 in the heat exchanger or is overheating then the flow pipe will be at that temp. It just won’t reach the rads. I wonder if somebody turned down the kw output when your first heat exchanger was acting up?

    Edit. I assume you’re giving the boiler a couple of hours to heat up because some WB boilers have a function on start up that the boiler fires for 15/20 mins and dosent go above 45 degrees.

    But the flow pipe isn't at 80 ...I'm checking the flow pipe just as it leaves the boiler and yes the measurements were made after the boiler had been running for hours


  • Moderators, Home & Garden Moderators Posts: 6,380 Mod ✭✭✭✭Wearb


    If it were an oil boiler I would suspect air or sludge in boiler at this stage.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    But the flow pipe isn't at 80 ...I'm checking the flow pipe just as it leaves the boiler and yes the measurements were made after the boiler had been running for hours

    To me it sounds like the boiler kw output is turned down. Therefore let’s say, the boiler is firing at 10% max power, so that’s never gonna reach temp.


  • Registered Users, Registered Users 2 Posts: 2,573 ✭✭✭Fingers Mcginty


    Wearb wrote: »
    If it were an oil boiler I would suspect air or sludge in boiler at this stage.

    It's a gas condensing boiler. I had my system flushed prior to install 2 years ago. It was flushed again last march after the heat exchanger was replaced and it's just had another power flush. The system was clean but bosch recommended that as the first port of call.


  • Registered Users, Registered Users 2 Posts: 2,573 ✭✭✭Fingers Mcginty


    Dtp1979 wrote: »
    To me it sounds like the boiler kw output is turned down. Therefore let’s say, the boiler is firing at 10% max power, so that’s never gonna reach temp.

    If that were the case why is the temp display on the boiler actually reading 80 degrees when it's set at max and then trips out for over temp? :)


  • Moderators, Home & Garden Moderators Posts: 6,380 Mod ✭✭✭✭Wearb


    HX is getting to temp at the gauge but not at the outlet.....hmmmm

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 2,573 ✭✭✭Fingers Mcginty


    Wearb wrote: »
    HX is getting to temp at the gauge but not at the outlet.....hmmmm

    exactly


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    If that were the case why is the temp display on the boiler actually reading 80 degrees when it's set at max and then trips out for over temp? :)

    Sorry. Long long weekend. Could be a combination. Of what I said or a faulty pump. I’ve seen those pumps go before. Not cheap either. Get on to the warranty


  • Registered Users, Registered Users 2 Posts: 2,573 ✭✭✭Fingers Mcginty


    they changed the pump last week.
    Up in a few hrs for work. Talk later and i really appreciate all the feedback lads. :)


  • Moderators, Home & Garden Moderators Posts: 6,380 Mod ✭✭✭✭Wearb


    exactly

    I think at this stage (and as already been suggested) it's a warranty call.
    They might be able to check to see if a proper flush was done, proper inhibitor added and no fresh water being introduced.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 2,573 ✭✭✭Fingers Mcginty


    Wearb wrote: »
    I think at this stage (and as already been suggested) it's a warranty call.
    They might be able to check to see if a proper flush was done, proper inhibitor added and no fresh water being introduced.

    Flush done 3 times already with rust inhibit added. No new water is being introduced as the top up valve is closed and it's maintaining 1.5 bar


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Flush done 3 times already with rust inhibit added. No new water is being introduced as the top up valve is closed and it's maintaining 1.5 bar

    Theres a chance you had a poor flush done 3 times. My money is on the pump though


  • Registered Users, Registered Users 2 Posts: 2,573 ✭✭✭Fingers Mcginty


    Dtp1979 wrote: »
    Theres a chance you had a poor flush done 3 times. My money is on the pump though

    No they did it properly and the recirculation pump has been changed already.