VOKERA Mynute 25 EHE - pressure is too high

  • 04-12-2017 10:13pm
    #1
    Registered Users, Registered Users 2 Posts: 32


    Hi,
    This problem is my own doing. The pressure was very low on my boiler (VOKERA Mynute 25 EHE) recently so I topped it up.Have done this before and it was fine but this time it went too high on me before I realised. When system is off it's at 2 and when heating is on after 15 mins it reaches 3 i.e. the red mark. I bled a radiator to get it back down to 1 but it has crept back up.
    Any advice would be appreciated.
    Thanks


Comments

  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    If it's creeping back up, the filling valve is not fully closed or passing water to the heating system when closed.


  • Registered Users, Registered Users 2 Posts: 32 caramel08


    Okay thanks. I'll check that.


  • Registered Users, Registered Users 2 Posts: 2 sizthediz50