Oil boiler over temp tripping

  • 30-10-2017 7:02pm
    #1
    Registered Users, Registered Users 2 Posts: 699 ✭✭✭


    Hi

    I have an oil boiler that's tripping out all the time on the over temp switch. When I press the OT switch back in it starts up again.

    The radiators are getting red hot before the boiler trips. I have set the thermostat on the boiler to 60 degrees (from 90) but it doesn't seem to control the temp of the boiler at all and it just keeps heating until it trips.

    Any idea what it might be? Is it the thermostat? Everything seems to be working normally in that the radiators at heating it's just that they are getting too hot.

    Thanks a mill for the advice.


Comments

  • Registered Users, Registered Users 2 Posts: 8,565 ✭✭✭K.Flyer


    Most likely the thermostat on the boiler needs replacing.


  • Registered Users, Registered Users 2 Posts: 699 ✭✭✭davegilly


    Cheers. That seems like a handy enough job to replace? I will have a look at it tomorrow and see if I can remove it. Thanks for help.


  • Registered Users, Registered Users 2 Posts: 699 ✭✭✭davegilly


    K.Flyer wrote: »
    Most likely the thermostat on the boiler needs replacing.
    That was it, replaced and fixed. Thanks for your help