Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Best solution to insulate suspended floorboards

  • 30-12-2016 1:53pm
    #1
    Registered Users, Registered Users 2 Posts: 272 ✭✭


    Hi,

    Any recommendation on insulation of suspended floorboards for a 3 bed semi detached. The area is c55 sqm.

    I am looking for a good solution without breaking the bank.
    Could I avail of the seai grants?

    Thanks


Comments

  • Moderators, Home & Garden Moderators Posts: 10,146 Mod ✭✭✭✭BryanF




  • Registered Users, Registered Users 2 Posts: 407 ✭✭smjm


    This set of 3 videos might be of interest to you: https://www.youtube.com/playlist?list=PLH911xvwsOXaPhEfY6O3TwokpKK6O97YX

    The comments are worth a read too.


  • Registered Users, Registered Users 2 Posts: 272 ✭✭cargen


    Thanks for the links, very helpful.

    Any idea of the costs in Dublin area for this type of work. Could I avail of seai grants.


  • Registered Users, Registered Users 2 Posts: 407 ✭✭smjm


    cargen wrote: »
    Thanks for the links, very helpful.

    Any idea of the costs in Dublin area for this type of work. Could I avail of seai grants.
    No idea on costs I'm afraid.

    It doesn't look like you could get a grant either: http://www.seai.ie/Grants/Better_energy_homes/Better_Energy_FAQ/Homeowner%20FAQ/What-type-of-work-can-I-get-a-grant-for-.html


  • Registered Users, Registered Users 2 Posts: 12,888 ✭✭✭✭Calahonda52


    have a look here for technique:
    https://www.nsai.ie/S-R-54-2014-Code-of-Practice.aspx

    Cost is very difficult to give as you give no ideas as to the existing flooring type and the number of rooms etc.

    In passing, this job is quite difficult to get done RIGHT. the main problem is getting the airtightness right to stop the air passing THROUGH the new insulation

    “I can’t pay my staff or mortgage with instagram likes”.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 272 ✭✭cargen


    have a look here for technique:
    https://www.nsai.ie/S-R-54-2014-Code-of-Practice.aspx

    Cost is very difficult to give as you give no ideas as to the existing flooring type and the number of rooms etc.

    In passing, this job is quite difficult to get done RIGHT. the main problem is getting the airtightness right to stop the air passing THROUGH the new insulation

    Thanks,
    Floor area is c50 sqm , 3 rooms and entrance.
    Floor is just made of floorboards no carpet or anything else on top.

    It would be great to have a high level idea of the cost.


  • Registered Users, Registered Users 2 Posts: 1,915 ✭✭✭micar


    I'm looking at doing the same thing.

    Choice between using rockwool, sheeps wool or polyurethane sheets(Kingspan, quinntherm etc)

    Still Undecided what to use and which would be easier to install.

    You need to look at all, determine the u value required and cost of each method to achieve this.

    Need to use air tightness membrane between insulation and floorboards.

    Depending on insulation, you'll need to use netting or clips or nails to hold the insulation in place.

    The membrane will need to be taped to the sides of the wall behind the skirting board.

    You cannot block the vents.


  • Registered Users, Registered Users 2 Posts: 962 ✭✭✭James 007


    It will depend on how the work can be done. Do the floor boards need to come up or is it possible to gain access under the floor by just removing some floor boards and working from underneath. I have done this before, it is a messy job especially if using fibreglass insulation and not easy if access is restricted. Essentially a person lying on ones back under a floor with an access space height of less than 0.5m.

    If the floor boards need to come up can they be taken up without damage to them. Usually old houses the floors are fixed down using iron nail fixings. These are difficult to prise up without damage to the floorboards. Do you expect to lift all the floor boards for the works, if so all the furniture would have to be removed too from the rooms.


  • Registered Users, Registered Users 2 Posts: 12,888 ✭✭✭✭Calahonda52


    micar wrote: »
    I'm looking at doing the same thing.

    Choice between using rockwool, sheeps wool or polyurethane sheets(Kingspan, quinntherm etc)

    Still Undecided what to use and which would be easier to install.

    You need to look at all, determine the u value required and cost of each method to achieve this.

    Need to use air tightness membrane between insulation and floorboards.

    Depending on insulation, you'll need to use netting or clips or nails to hold the insulation in place.

    The membrane will need to be taped to the sides of the wall behind the skirting board.

    You cannot block the vents.

    Good stuff here Micar.
    Just the one I bolded needs a bit more thought, IMO iff using non rigid insulation.

    It the A/T layer is positioned as you suggest, which has been conventional practice since we moved out of the caves in Africa, then the air blowing through the space underneath with have unfettered access to blow THROUGH the insulation, thereby reducing, or even eliminating the U value.

    If you think about it for a moment, and ignore the rain issue, a roof insulated in the same way always has a windproof layer on the cold side....

    If this logic is correct, then the rigid insulation, as suggested by yourself above gets better performance for your buck.

    I agree with James 007 re the practical issues, been that soldier, hence It brings us back to properly done rigid.

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 9,605 ✭✭✭gctest50


    Not be simpler ( from an airtightness POV ) to :

    drop the floor ~ 100 or whatever mm,
    sheet it,
    seal the gaps between the sheets and wall,
    put down floor insulation that can take the load,
    sheet over that and then flooring ?

    ( obv. take care of underfloor vents, dpc, etc )


    instead of staples and netting and airleaks and air bypassing your bits of solid you've cut up


  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 10,146 Mod ✭✭✭✭BryanF


    micar wrote: »
    I'm looking at doing the same thing.

    Choice between using rockwool, sheeps wool or polyurethane sheets(Kingspan, quinntherm etc)

    Still Undecided what to use and which would be easier to install.

    You need to look at all, determine the u value required and cost of each method to achieve this.

    Need to use air tightness membrane between insulation and floorboards.

    Depending on insulation, you'll need to use netting or clips or nails to hold the insulation in place.

    The membrane will need to be taped to the sides of the wall behind the skirting board.

    You cannot block the vents.
    Anything but PIR (kingspan type) - the 'wools' are just easier to get into gaps etc.

    I used Breathable roof membrane instead of netting

    PIR can be handy underneath the floors at the rising walls to help reduce thermal bridging, a lot of foam would be required to ensure continuity.

    You'll find air-tightness tape is great for membrane to membrane but flexible gun sealant is easier for existing wall to membrane junctions.

    It's important the person doing this work understands the final requirements of the timber floor.


  • Registered Users, Registered Users 2 Posts: 4,528 ✭✭✭BoardsMember


    gctest50 wrote: »
    Not be simpler ( from an airtightness POV ) to :

    drop the floor ~ 100 or whatever mm,
    sheet it,
    seal the gaps between the sheets and wall,
    put down floor insulation that can take the load,
    sheet over that and then flooring ?

    ( obv. take care of underfloor vents, dpc, etc )


    instead of staples and netting and airleaks and air bypassing your bits of solid you've cut up

    That looks to me less reliant on someone getting a nasty job done correctly, i.e. you will not necessarily discover the "missed bits" on the other approaches suggested, whereas this method looks to be easier & more reliable.


  • Registered Users, Registered Users 2 Posts: 12,888 ✭✭✭✭Calahonda52


    That looks to me less reliant on someone getting a nasty job done correctly, i.e. you will not necessarily discover the "missed bits" on the other approaches suggested, whereas this method looks to be easier & more reliable.

    Dropping the floor joists may mean having to drop the dpc inside the house lower than the dpc on the walls so that is an important detail to be considered.
    The external wall vents may need to be redone, and possibly a lot of wiring and CH and other plumbing.

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 962 ✭✭✭James 007


    Dropping the floor joists may mean having to drop the dpc inside the house lower than the dpc on the walls so that is an important detail to be considered.
    The external wall vents may need to be redone, and possibly a lot of wiring and CH and other plumbing.

    Sometimes external vents are just one brick high above ground level or less so this may not be possible. Also fire hearth may be supported on main timbers/joists so this may also require adjusting


  • Registered Users, Registered Users 2 Posts: 233 ✭✭Heartbreak Hank


    Sorry if there is a more up to date thread on this subject than this one.


    Is there a minimum void required below the insulation? In my house (1950s/1960s semi d), based on lifting a couple boards, I have ~200 mm from top of joist to ground level. The joist is 110mm, so there is 90mm below the joist. I was intending to use 100 mm PIR on battens between the joists leaving a ventilated depth of 100 mm. Is this a condensation / rot risk?


Advertisement