Gas boiler issue

  • 01-12-2016 9:51pm
    #1
    Registered Users, Registered Users 2 Posts: 3,068 ✭✭✭


    Hi

    I have a volters 16E gas boiler. Over the last few days been having issues as it wont ignite. I had some dude come and have a look. He bled the rads. His of the impression that the issue is when i put upstairs on first the pressure drops..when i put downstairs on first, wait for spark and then put on upstairs it works fine and pressure is over 1. If i put upstairs on first the pressure is 0.2 and nowt happens.

    He thinks it could be the cold weather and simething about upstairs needing more water/🤒Pressure ..i think

    What you think lads..im lost as to what it is..


Comments

  • Registered Users, Registered Users 2 Posts: 1,709 ✭✭✭wiz569


    When both zones are open/calling for heat what is the system pressure?


  • Registered Users, Registered Users 2 Posts: 3,068 ✭✭✭Specialun


    wiz569 wrote: »
    When both zones are open/calling for heat what is the system pressure?


    When both zones are on its a good solid 1 if not big higher..upstairs on its own 0.2 and red light comes on and doesnt ignite


  • Registered Users, Registered Users 2 Posts: 1,709 ✭✭✭wiz569


    Specialun wrote: »
    When both zones are on its a good solid 1 if not big higher..upstairs on its own 0.2 and red light comes on and doesnt ignite

    Is that a one when the boiler is running and hot or is that when both zones are open but boiler off ,

    It should be the same pressure regardless of what zones are open to be honest and that pressure should be about 1 to 1.5 when cold, not quite sure why you are getting different pressures as the whole system should be as one,

    You really need an RGI plumber to check it out properly.