Baxi Megaflo Boiler Error

  • 13-03-2016 8:04pm
    #1
    Closed Accounts Posts: 18,958 ✭✭✭✭


    Hi,

    I have a Baxi Megaflo HE IE boiler. It is gas boiler. I put it in a few years ago and get it serviced every year

    Anyway it has stopped working. I checked it and it is flashing E1 and then 64 so I guess that is E164? I don't see anything in manual?

    I just see this list:
    http://www.baxi.co.uk/trade-area/support/error-codes.htm

    Any idea how I could fix?


Comments

  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Shefwedfan wrote: »
    Hi,

    I have a Baxi Megaflo HE IE boiler. It is gas boiler. I put it in a few years ago and get it serviced every year

    Anyway it has stopped working. I checked it and it is flashing E1 and then 64 so I guess that is E164? I don't see anything in manual?

    I just see this list:
    http://www.baxi.co.uk/trade-area/support/error-codes.htm

    Any idea how I could fix?

    Waa the boiler making any banging or hissing noise recently?


  • Registered Users, Registered Users 2 Posts: 2,880 ✭✭✭2012paddy2012


    I have exact same boiler same as yours ....did you try holding reset knob for few seconds ..my E error meant bleed rads ..got it serviced yesterday all well again ..I have a list of E ...faults ..just checked it ...that number on yours is not on list tho ..sorry


  • Closed Accounts Posts: 18,958 ✭✭✭✭Shefwedfan


    Dtp1979 wrote: »
    Waa the boiler making any banging or hissing noise recently?

    The boiler is in attic so can't really hear it......


  • Closed Accounts Posts: 18,958 ✭✭✭✭Shefwedfan


    I have exact same boiler same as yours ....did you try holding reset knob for few seconds ..my E error meant bleed rads ..got it serviced yesterday all well again ..I have a list of E ...faults ..just checked it ...that number on yours is not on list tho ..sorry

    I tried that, turned it off and on, same error came up

    Tried the rest and nothing

    Checked water pressure and it is ok

    The pump in the boiler seems to be going but it is not firing


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Shefwedfan wrote: »
    The boiler is in attic so can't really hear it......

    Usually means overheating I'm nearly sure. Coujd be air build up because of the boiler location.
    Could be sludge either. Was the system powerflushed before the new boiler was installed?
    Is there a magnetic filter at the boiler?


  • Advertisement
  • Closed Accounts Posts: 18,958 ✭✭✭✭Shefwedfan


    Dtp1979 wrote: »
    Usually means overheating I'm nearly sure. Coujd be air build up because of the boiler location.
    Could be sludge either. Was the system powerflushed before the new boiler was installed?
    Is there a magnetic filter at the boiler?

    System was emptied, what is power flush? as I dont know I guess it wasnt done

    What does magnetic filter look like? :p


  • Registered Users, Registered Users 2 Posts: 1,884 ✭✭✭Robbie.G


    Shefwedfan wrote: »
    I tried that, turned it off and on, same error came up

    Tried the rest and nothing

    Checked water pressure and it is ok

    The pump in the boiler seems to be going but it is not firing

    It's air locked or the pumps jammed on the top of the older ones there is an auto air vent beside the flue bend make sure that's open other than that you will need an rgi to look at it


  • Closed Accounts Posts: 18,958 ✭✭✭✭Shefwedfan


    Robbie.G wrote: »
    It's air locked or the pumps jammed on the top of the older ones there is an auto air vent beside the flue bend make sure that's open other than that you will need an rgi to look at it

    Thanks will have a look


  • Closed Accounts Posts: 18,958 ✭✭✭✭Shefwedfan


    Ok, no idea what I am at, there is valve at top but looks to be able to let air out

    ANy idea how much it would cost to get it fixed?


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Shefwedfan wrote: »
    Ok, no idea what I am at, there is valve at top but looks to be able to let air out

    ANy idea how much it would cost to get it fixed?

    Post a few pics


  • Advertisement
  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    E164 is a water flow switch error on this model, which maybe either:
    a) too low water pressure
    b) failed pump
    c) failed/blocked water flow switch/filters
    d) circulation issues (dirt, blocked filters, power flush required etc.)

    You can top up your water to a cold fill pressure of 1bar and reset the boiler, if it's b-d you will need an RGI to diagnose and repair


  • Closed Accounts Posts: 18,958 ✭✭✭✭Shefwedfan


    Quick update, had a look around one of evenings during the week, found a valve and let a little squirt of water out, bingo it fired up....happy days

    Thanks everyone for advice