crossed neutrals

  • 06-02-2016 5:16pm
    #1
    Registered Users, Registered Users 2 Posts: 586 ✭✭✭


    Maybe a silly question but say for example you had a crossed live/neutral on a lighting circuit /Could would this cause your esb meter to run up a large bill?


Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    SC024 wrote: »
    Maybe a silly question but say for example you had a crossed live/neutral on a lighting circuit /Could would this cause your esb meter to run up a large bill?

    "Crossed" as in connected to each other?

    No.
    You are describing a "short circuit". This generally causes a flash and a bang and should trip the upstream MCB.


  • Closed Accounts Posts: 3,478 ✭✭✭eeguy


    If the wires are touching then no.

    However if "something" is bridging the wires then possibly, on the condition that 1, the something is not earthed, 2 the something has a resistance such that the current flowing through it is less that the breaker rating for that particular circuit and 3 the something is capable of dissipating the power dropped across it.

    Very unlikely and I'm open to correction on any of these points.


  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    think op means reversed polarity,this shouldnt have any bearing on meter reading(needs to be checked though)


  • Posts: 5,238 ✭✭✭ [Deleted User]


    AC isn't polarised. I'd suspect the wiring colour code unconventional.


  • Registered Users, Registered Users 2 Posts: 586 ✭✭✭SC024


    Thank guys :)


  • Advertisement
  • Closed Accounts Posts: 3,478 ✭✭✭eeguy


    AC isn't polarised. I'd suspect the wiring colour code unconventional.

    Not universally true. You can get away with it in basic devices,, but beyond that you'd want to make sure you have your wiring done correctly.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    eeguy wrote: »
    Not universally true. You can get away with it in basic devices,, but beyond that you'd want to make sure you have your wiring done correctly.

    What 2 wire AC devices would be polarity sensitive, since polarity doesnt really exist in a 2 wire AC supply?


  • Closed Accounts Posts: 3,478 ✭✭✭eeguy


    Bruthal wrote: »
    What 2 wire AC devices would be polarity sensitive, since polarity doesnt really exist in a 2 wire AC supply?

    Audio stuff and some mains filtering devices and non isolated power supplies can be sensitive depending on design. It's also a safety issue. Fuses are usually on the live and reversing polarity can bypass the fuse.


  • Moderators, Motoring & Transport Moderators Posts: 6,522 Mod ✭✭✭✭Irish Steve


    eeguy wrote: »
    Audio stuff and some mains filtering devices and non isolated power supplies can be sensitive depending on design. It's also a safety issue. Fuses are usually on the live and reversing polarity can bypass the fuse.

    Oh Dear.

    The Fuse is NOT bypassed, but in some circumstances, if the fuse fails and is in the neutral line, there is the potential for 240V to be present on components of the device, and in some fault situations, depending on external protection, current could flow to earth, which is not desirable, and could indeed present a safety hazard.

    Shore, if it was easy, everybody would be doin it.😁



  • Closed Accounts Posts: 3,478 ✭✭✭eeguy


    Oh Dear.

    The Fuse is NOT bypassed, but in some circumstances, if the fuse fails and is in the neutral line, there is the potential for 240V to be present on components of the device, and in some fault situations, depending on external protection, current could flow to earth, which is not desirable, and could indeed present a safety hazard.

    Yep that's what I meant.


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    eeguy wrote: »
    Audio stuff and some mains filtering devices and non isolated power supplies can be sensitive depending on design.
    With only 2 wires though, there is not much reference to anything. Audio stuff is likely to have an isolating supply.

    It's also a safety issue. Fuses are usually on the live and reversing polarity can bypass the fuse.
    I`m more talking about in terms of operation. Other countries appliance plugs can be plugged in either way around. Connect a neutralized house up with L and N the wrong way around into the esb fuse unit and its not going to be great though.


  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    Presumably by crossed neutrals he means a borrowed neutral, i.e. a neutral taken from a different circuit than the phase conductor.

    Actually, rereading I'm not 100% certain that this is what was meant - it's not entirely clear.


  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    Presumably by crossed neutrals he means a borrowed neutral, i.e. a neutral taken from a different circuit than the phase conductor.

    Actually, rereading I'm not 100% certain that this is what was meant - it's not entirely clear.


  • Closed Accounts Posts: 3,478 ✭✭✭eeguy


    Bruthal wrote: »

    I`m more talking about in terms of operation. Other countries appliance plugs can be plugged in either way around. Connect a neutralized house up with L and N the wrong way around into the esb fuse unit and its not going to be great though.

    Yep buy they use double pole fusing, lower amp MCBs and different domestic wiring. My point is that it's not good practice to simply say that polarity doesnt matter.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Risteard81 wrote: »
    Presumably by crossed neutrals he means a borrowed neutral, i.e. a neutral taken from a different circuit than the phase conductor.

    Actually, rereading I'm not 100% certain that this is what was meant - it's not entirely clear.

    L and N swapped around Id say they mean.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    eeguy wrote: »
    Yep buy they use double pole fusing, lower amp MCBs and different domestic wiring. My point is that it's not good practice to simply say that polarity doesnt matter.
    Nobody said it doesnt matter though.

    The plugs in continental appliances have no fuses.


  • Posts: 5,238 ✭✭✭ [Deleted User]


    Polarity does matter but AC doesn't have one (it reverses at 50Hz) . Wiring convention matters and for these purposes (switching/protection) we say (in this country with single pole MCBs) that electricity comes in a live and returns the neutral. In reality the electrons are vibrating not flowing like a DC circuit that does have a polarity.
    Yes there's a difference in potential WTE that is sensitive to some applications but lights are not one of these.


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    Polarity does matter in a TN-C country like ours.
    The N phase is always going to be at or about earth potential and in older builds neutrals were starred and commoned all over the place.
    Mixing a live potential on to this would cause all sorts of weird stuff to happen.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Steve wrote: »
    Polarity does matter in a TN-C country like ours.
    The N phase is always going to be at or about earth potential and in older builds neutrals were starred and commoned all over the place.
    Mixing a live potential on to this would cause all sorts of weird stuff to happen.
    True, but as was said, it has not been stated that it doesnt matter. More that polarity doesnt really exist in AC in the same sense as in DC. Plug in the tv, vacuum cleaner, drill, with L and N reversed, and they all still work the same.


    Great minds, (or fools)
    Bruthal wrote: »
    Connect a neutralized house up with L and N the wrong way around into the esb fuse unit and its not going to be great though.


  • Posts: 5,238 ✭✭✭ [Deleted User]


    Lights and ESB meters aren't "AC polarity" sensitive devices.

    If you're worried just turn the bulb around.


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Lights and ESB meters aren't "AC polarity" sensitive devices.

    If you're worried just turn the bulb around.
    Well no, but you wouldnt want an esd land man/woman coming and connecting the supply cable in reverse at the fuse unit.

    Also, on the older type disc meters, they will reverse if the supply and load are reversed, since the current direction at any instant on the phase is now opposite with reference to the current through the voltage detection part.


  • Posts: 5,238 ✭✭✭ [Deleted User]


    Agreed.
    However then the bills would reduce not increase and you'd notice a supply fault fairly lively.

    The new supply meter rollout in the UK was prompted by customers with backward spinners due to PV arrays.


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    The old disc meters couldn't do that, there was only one in / one out. Unless you reversed line and load, they would always measure.

    One of my Kevin St lecturers many many years ago was ex ESB and he told stories of things people tried to do to 'fool' meters.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal



    The new supply meter rollout in the UK was prompted by customers with backward spinners due to PV arrays.

    That,s right yea. It should come along here in about 2150 id say.


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    The new supply meter rollout in the UK was prompted by customers with backward spinners due to PV arrays.

    How did that work?

    Just curios, I know it's illegal here.

    Wouldn't have thought any PV source could generate enough to make a difference.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Steve wrote: »
    How did that work?

    Just curios, I know it's illegal here.

    Wouldn't have thought any PV source could generate enough to make a difference.

    Well if you have a 2kw output from home generation, and a load of 500 watts on in the house, its backwards meter time. So they install meters to properly measure the grid fed surplus.


  • Posts: 5,238 ✭✭✭ [Deleted User]


    Dunno exactly I never had one. I've just seen reports on other forums of people being unavailable as long as they could manage after reporting the fault when asked to facilitate engineers to "upgrade the meter".

    PV will produce rated output under STC all you'd have to do is reduce the import/loads.


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    Bruthal wrote: »
    Well if you have a 2kw output from home generation, and a load of 500 watts on in the house, its backwards meter time. So they install meters to properly measure the grid fed surplus.

    You're right, sorry, I only ever looked at it in financial rather than electrical terms - It will always will be a nett loss due to cost of equipment vs what it you could possibly sell back to the grid (if it was legal) over its lifetime.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Steve wrote: »
    You're right, sorry, I only ever looked at it in financial rather than electrical terms - It will always will be a nett loss due to cost of equipment vs what it you could possibly sell back to the grid (if it was legal) over its lifetime.

    It would be interesting here, if ye did send the meter in reverse, the fraud squad would probably be out.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    Yeah, jail time for sure.

    Worse than importing garlic but not as bad as ripping off a country for 60 bill... :D


  • Posts: 5,238 ✭✭✭ [Deleted User]


    We will make electricity so cheap that only the rich will burn candles.


    The grid doesn't want the competition. Closed shop.
    And the Minister for energy doesn't feel obliged to meet our EU renewable targets.

    I've a back room fulla second hand gear cheap as chips and fairly high end with more on the way waiting for me to have the time to fit it. No install costs, no mandatory Irish spec. overpriced gubbins, ex service batteries, never used other than for system testing.
    Used grid tie gear goes for next to nothing because it's not eligible for for re-use in grid tie and nobody wants 48V stuff because it's too big for boats and campers. I promise I'll splash out on new protective breakers though. ;)


  • Posts: 5,238 ✭✭✭ [Deleted User]


    Perfectly legal give it to them for free by the way if it's signed off on, which some people are encouraged to do for BER/passive ratings.


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    How would that work?

    Backspinning a meter is reducing your bill. Same as selling back.. illegal?


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Steve wrote: »
    How would that work?

    Backspinning a meter is reducing your bill. Same as selling back.. illegal?
    Yea but if you spun it back due to surplus generation, in reality you have reduced their bill. Get them to install a smart meter.


  • Posts: 5,238 ✭✭✭ [Deleted User]


    I'm not selling it I'm using it.
    Minimum import.

    It's also modular so I won't be obliged to install services in my next house which makes the possibilities interesting.


  • Advertisement
  • Posts: 5,238 ✭✭✭ [Deleted User]


    Steve wrote: »
    Backspinning a meter is reducing your bill. Same as selling back


    Units off the import meter are worth far more than on the export meter.
    They paid less than they charged.