Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Boiler in utility room.

  • 23-10-2015 9:11pm
    #1
    Banned (with Prison Access) Posts: 2,943 ✭✭✭


    Hi

    Just moved in to a rented house and the oil boiler (firebird S 90-120 ) is in the utility room near washing machine and dryer etc.

    Do people think this is a bit strange / unhygienic ?

    When the boiler is turned on, the smell in the utility room is not too pleasant..........but that may be because the boiler has not been turned on in months maybe.


«13

Comments

  • Registered Users, Registered Users 2 Posts: 1,492 ✭✭✭roy rodgers


    Hi

    Just moved in to a rented house and the oil boiler (firebird S 90-120 ) is in the utility room near washing machine and dryer etc.

    Do people think this is a bit strange / unhygienic ?

    When the boiler is turned on, the smell in the utility room is not too pleasant..........but that may be because the boiler has not been turned on in months maybe.

    There should be no smell. What does is smell like

    Get the landlord to get the boiler checked out and get a carbon monoxide alarm for your self!


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    you should have no smell from your boiler when its in use get onto to your landlord to have this boiler serviced asap

    for your safety don't use it until this is done


  • Banned (with Prison Access) Posts: 2,943 ✭✭✭from_atozinc


    There should be no smell. What does is smell like

    Get the landlord to get the boiler checked out and get a carbon monoxide alarm for your self!

    Hi. Thanks for reply. It just smells like oil / fuel.

    Is a carbon monoxide alarm definitely the thing I need ?


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Hi. Thanks for reply. It just smells like oil / fuel.

    Is a carbon monoxide alarm definitely the thing I need ?

    A good service is what you need and yes, a carbon monoxide alarm


  • Banned (with Prison Access) Posts: 2,943 ✭✭✭from_atozinc


    Dtp1979 wrote: »
    A good service is what you need and yes, a carbon monoxide alarm


    Thanks for input.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,492 ✭✭✭roy rodgers


    Sounds like the flue is leaking fumes into the room not a good idea. The carbon monoxide alarm will only tell you that for sure but it really needs to looked at asap


  • Banned (with Prison Access) Posts: 2,943 ✭✭✭from_atozinc


    Sounds like the flue is leaking fumes into the room not a good idea. The carbon monoxide alarm will only tell you that for sure but it really needs to looked at asap


    Carbon monoxide alarm has been installed for over 24 hours now and no alarm - and I tested it and all that.

    So does this mean there is nothing wrong with boiler ?


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Carbon monoxide alarm has been installed for over 24 hours now and no alarm - and I tested it and all that.

    So does this mean there is nothing wrong with boiler ?

    No that just means it's not leaking carbon monoxide. I've seen new boilers pump out huge levels of CO.


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    Carbon monoxide alarm has been installed for over 24 hours now and no alarm - and I tested it and all that.

    So does this mean there is nothing wrong with boiler ?

    Incorrect,carbon monoxide alarms will not alert you of low levels of carbon monoxide,carbon monoxide alarms keep people from dying,they dont eliminate all health risks.
    there are numerous studies saying that low levels of carbon monoxide cause health problems


  • Banned (with Prison Access) Posts: 2,943 ✭✭✭from_atozinc


    Dtp1979 wrote: »
    No that just means it's not leaking carbon monoxide. I've seen new boilers pump out huge levels of CO.


    I don't get your post. I thought Carbon monoxide was the same as CO.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    I don't get your post. I thought Carbon monoxide was the same as CO.

    It is. Just cause the aka doesn't go off doesn't mean your burner is burning properly. As in if a new boiler was installed, was pumping out dangerous fumes then it's potentially dangerous. if a seal broke inside, the fumes would probably kill somebody in the house


  • Banned (with Prison Access) Posts: 2,943 ✭✭✭from_atozinc


    Dtp1979 wrote: »
    It is. Just cause the aka doesn't go off doesn't mean your burner is burning properly. As in if a new boiler was installed, was pumping out dangerous fumes then it's potentially dangerous. if a seal broke inside, the fumes would probably kill somebody in the house

    Pardon my ignorance.

    If it's not burning properly, then it should be giving off fumes which in turn should set off the Carbon monoxide alarm ?


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    A carbon monoxide alarm will not go off under 30 ppm and even from 30 ppm to 70 ppm the alarm may take a long time to go off.
    You could have 25 ppm in the room and the alarm will not go off.this can cause health problems


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    Your boiler should be serviced in conjunction with a flue gas analyzer and tested for leaks with a flue gas analyser and a room test done for co.,its good to have a carbon monoxide alarm in place too as it may save your life


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Pardon my ignorance.

    If it's not burning properly, then it should be giving off fumes which in turn should set off the Carbon monoxide alarm ?

    only if the fumes are leaked into the room


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    the best way to approach co is no level is a good level

    have a read of this link to give u an understanding of what you dealing with

    http://www.carbon-monoxide-poisoning.com/article1-co-levels.html


  • Registered Users, Registered Users 2 Posts: 1,775 ✭✭✭JamesM


    You probably have a slight oil leak or weep. A service is a good idea and should sort it out.
    Jim.


  • Banned (with Prison Access) Posts: 2,943 ✭✭✭from_atozinc


    JamesM wrote: »
    You probably have a slight oil leak or weep. A service is a good idea and should sort it out.
    Jim.

    Thanks Jim.


  • Registered Users, Registered Users 2 Posts: 17,165 ✭✭✭✭astrofool


    CO itself is odourless, so if there's a smell in the room, it's likely coming from something else (not that CO may not be present as well). Does it smell like the oil is leaking somewhere?

    A good CO alarm should flash when there's low levels of CO and flashing gets faster as the CO level goes up.


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    astrofool wrote: »
    CO itself is odourless, so if there's a smell in the room, it's likely coming from something else (not that CO may not be present as well). Does it smell like the oil is leaking somewhere?

    A good CO alarm should flash when there's low levels of CO and flashing gets faster as the CO level goes up.

    A good co alarm will not go off if co is less than 30ppm


  • Advertisement
  • Banned (with Prison Access) Posts: 2,943 ✭✭✭from_atozinc


    I'm wondering though, hearing has not been on in about 6 months. So would this contribute to the smell a bit.


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    simple answer no


  • Registered Users, Registered Users 2 Posts: 455 ✭✭Jen44


    I just bought a house with an oil boiler always had gas before. The first time we put the heating on there was a fuel kinda of smell, the boiler had just been serviced before we moved in. Anyhow after a day or so of the heating coming on and off there has been no further issue with smell. The house was vacant for a year before we moved in


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    Jen44 wrote: »
    I just bought a house with an oil boiler always had gas before. The first time we put the heating on there was a fuel kinda of smell, the boiler had just been serviced before we moved in. Anyhow after a day or so of the heating coming on and off there has been no further issue with smell. The house was vacant for a year before we moved in

    Are you certain it has been serviced or just been told it was recently serviced? Do you have a service report?

    It no to the above, it might be better having it looked at.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 47 vrrv


    Shouldn't be a smell unless slightest of kerosene! Check it out!!!


  • Registered Users, Registered Users 2 Posts: 152 ✭✭Walter Becket


    Jen44 wrote: »
    I just bought a house with an oil boiler always had gas before. The first time we put the heating on there was a fuel kinda of smell, the boiler had just been serviced before we moved in. Anyhow after a day or so of the heating coming on and off there has been no further issue with smell. The house was vacant for a year before we moved in

    There is a seal that is sometimes repaired with aluminium tape during a service the glue on it can smell for a while.


  • Banned (with Prison Access) Posts: 2,943 ✭✭✭from_atozinc


    What tradesman would service an oil boiler ? or is the job just called a boiler specialist ?


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    If not through a recommendation, then Oftec.org is a good way to find a boiler technician. Or post your location here and we might be able to recommend someone.
    Just make sure that whoever does it, gives you a service report which should have an electronic printout of the combustion gasses properties attached.

    Please follow site and charter rules. "Resistance is futile"



  • Banned (with Prison Access) Posts: 2,943 ✭✭✭from_atozinc


    Wearb wrote: »
    If not through a recommendation, then Oftec.org is a good way to find a boiler technician. Or post your location here and we might be able to recommend someone.
    Just make sure that whoever does it, gives you a service report which should have an electronic printout of the combustion gasses properties attached.

    Thanks, but like, can a plumber service a boiler or is it someone else entirely ?

    And yeah, looking for a person that can service a boiler in the Galway area


  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    Most plumbers "can" service them, but not all of them have the modern equipment and training necessary to get the best out of your boiler. That was the reason for my long-winded reply; to help you identify what you need to look out for.

    I am in the opposite end of the country, but someone here may be able to recommend someone in your area.

    Please follow site and charter rules. "Resistance is futile"



  • Banned (with Prison Access) Posts: 2,943 ✭✭✭from_atozinc


    Wearb wrote: »
    Most plumbers "can" service them, but not all of them have the modern equipment and training necessary to get the best out of your boiler. That was the reason for my long-winded reply; to help you identify what you need to look out for.

    I am in the opposite end of the country, but someone here may be able to recommend someone in your area.

    Thanks again


  • Banned (with Prison Access) Posts: 2,943 ✭✭✭from_atozinc



    And yeah, looking for a person that can service a boiler in the Galway area


    Anyone have any recommendations here ?


  • Banned (with Prison Access) Posts: 2,943 ✭✭✭from_atozinc


    Anybody ever use this lad:

    http://www.theboilerman.ie/about/about.htm


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979



    How much for the service?


  • Banned (with Prison Access) Posts: 2,943 ✭✭✭from_atozinc


    Dtp1979 wrote: »
    How much for the service?

    85 Euro


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    85 Euro

    Ask how long a service takes.


  • Banned (with Prison Access) Posts: 2,943 ✭✭✭from_atozinc


    Dtp1979 wrote: »
    Ask how long a service takes.


    why , is there something fishy about the 85 Euro charge?


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    I would be worried that the combustion chamber, baffles and flue ways aren't properly cleaned. This is the most time consuming and dirtiest part of the service. This area isn't well mentioned on the website. Make out a list of half a dozen important questions to ask before hiring.

    Price seems ok.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    why , is there something fishy about the 85 Euro charge?

    Not necessarily but there's some Cowboys out there charging 80-90 euro and spending 20 mins servicing a boiler.


  • Banned (with Prison Access) Posts: 2,943 ✭✭✭from_atozinc


    Thanks DTP.

    I also have another issue. The radiators(oil) by and large work fine, they all heat up fine except for 2 of them.

    The 2 that don't heat up are upstairs, other radiators upstairs work fine.

    What happens these 2 radiators is only the bottom inch or so of the radiator gets hot, the rest does not get hot at all.

    Any ideas on this?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,205 ✭✭✭cruizer101


    That sounds like they need to be bled, easy enough job, plenty of videos on youtube explaining it.

    Basically there is big air bubble trapped in them which means the hot water is not filling it up, there is valve at the top which allows bleeding the air out.

    That said, only bottom inch or so sounds like a lot of air, I'm not plumber or that so maybe one can advise if that is normal.


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    Thanks DTP.

    I also have another issue. The radiators(oil) by and large work fine, they all heat up fine except for 2 of them.

    The 2 that don't heat up are upstairs, other radiators upstairs work fine.

    What happens these 2 radiators is only the bottom inch or so of the radiator gets hot, the rest does not get hot at all.

    Any ideas on this?

    Just bleed the radiator


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    Thanks DTP.

    I also have another issue. The radiators(oil) by and large work fine, they all heat up fine except for 2 of them.

    The 2 that don't heat up are upstairs, other radiators upstairs work fine.

    What happens these 2 radiators is only the bottom inch or so of the radiator gets hot, the rest does not get hot at all.

    Any ideas on this?

    Make sure you have enough pressure on the system, if its a sealed system. If its air in those rads, you will also have to re pressurise after bleeding so much air out, "bottom inch or so of the radiator gets hot"

    Please follow site and charter rules. "Resistance is futile"



  • Banned (with Prison Access) Posts: 2,943 ✭✭✭from_atozinc


    Wearb wrote: »
    Make sure you have enough pressure on the system, if its a sealed system. If its air in those rads, you will also have to re pressurise after bleeding so much air out, "bottom inch or so of the radiator gets hot"


    is the re pressurising a big job ?
    who can do it or whats involved etc


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    is the re pressurising a big job ?
    who can do it or whats involved etc

    Is it a sealed system? ie do you have a small tank in attic or an expansion vessel (red metal tank).

    Anyway it's not a big job.

    Please follow site and charter rules. "Resistance is futile"



  • Banned (with Prison Access) Posts: 2,943 ✭✭✭from_atozinc


    Wearb wrote: »
    Is it a sealed system? ie do you have a small tank in attic or an expansion vessel (red metal tank).

    Anyway it's not a big job.


    im not sure. sorry.


  • Banned (with Prison Access) Posts: 2,943 ✭✭✭from_atozinc


    cruizer101 wrote: »
    That sounds like they need to be bled, easy enough job, plenty of videos on youtube explaining it.

    Basically there is big air bubble trapped in them which means the hot water is not filling it up, there is valve at the top which allows bleeding the air out.

    That said, only bottom inch or so sounds like a lot of air, I'm not plumber or that so maybe one can advise if that is normal.



    I had a look at some YouTube videos and they all describe a key that has to be inserted to let the air out.

    I could not find any place to insert a key in my radiators.

    See attached picture. In thinking I need to twist the little screw here with a screwdriver to let the air out. But not sure. Radiator brand is Purmo.


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    im not sure. sorry.

    Perhaps a pic of the hot press might shed some light.

    Please follow site and charter rules. "Resistance is futile"



  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    I had a look at some YouTube videos and they all describe a key that has to be inserted to let the air out.

    I could not find any place to insert a key in my radiators.

    See attached picture. In thinking I need to twist the little screw here with a screwdriver to let the air out. But not sure. Radiator brand is Purmo.

    That is the bleed screw. Don't use it until you work out how the system top up works. The pic might help.

    When bleeding, turn the white part 180° so that the little hole is at bottom. Have a rag held beneath it. Then turn the silver screw about 270° anticlockwise and wait for the water. Then turn it back to where it was. Don't turn the bleed screw too far anticlockwise or it will pop out and then the fun will start.

    Please follow site and charter rules. "Resistance is futile"



  • Banned (with Prison Access) Posts: 2,943 ✭✭✭from_atozinc


    Wearb wrote: »
    That is the bleed screw. Don't use it until you work out how the system top up works. The pic might help.

    When bleeding, turn the white part 180° so that the little hole is at bottom. Have a rag held beneath it. Then turn the silver screw about 270° anticlockwise and wait for the water. Then turn it back to where it was. Don't turn the bleed screw too far anticlockwise or it will pop out and then the fun will start.


    ok, thanks.

    So essentially I don't need any special tool to bleed it, just a standard screwdriver, yeah ?


  • Advertisement