Siemens spc zone reading null

  • 17-09-2015 2:44am
    #1
    Registered Users, Registered Users 2 Posts: 5,401 ✭✭✭


    What does it mean when a zone on a Siemens spc panel is reading back a (null) value in the log? Is it just the resistance is somewhere between open and closed? Or something different?


Comments

  • Registered Users, Registered Users 2 Posts: 6,562 ✭✭✭kub


    If you have dual end of line resistors on that particular zone, then it cannot see the value of those resistors therefore you have an open tamper condition.


  • Registered Users, Registered Users 2 Posts: 5,401 ✭✭✭DublinDilbert


    Ahh ok, so its an issue with the tamper switch/circuit. There was two sensors on that zone and I split each onto a separate zone. So its either a break on one of the wires form the panel or at the tamper switch.

    I'm quite new to the Europlex/SPC, so i would of thought a "Tamper" would of been thrown like the other systems i've seen.