Gerkros Coseyman

  • 24-02-2015 4:25pm
    #1
    Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭


    Was called out to a breakdown on this. Fault was a PC.

    Here is my question; the stat -pictured- only turns on the circulating pump when the temperature rises to setting on the stat. This means that boiler has to be fired up and the water in the pipe that stat is connected to has to reach 20C (it was 30C I just turned it down to check.) before circulating pump cuts in. This seems strange to me.
    Any explanations please?

    339981.jpg

    Please follow site and charter rules. "Resistance is futile"



Comments

  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    pump overrun must have been having problems with nuisance lockouts on the high limit stat


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    Thanks Jim. It it normal to have boiler starting without circulating pump running? Heat has to travel DOWN this pipe to activate the pump.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    it will have a permanent live to keep pump running after clock time off this helps to dissipate the heat away from the boiler thus stop the hl stat from activating gerkros do have this issue seen a few if set above 65/70 trip the hl stat


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    jimf wrote: »
    it will have a permanent live to keep pump running after clock time off this helps to dissipate the heat away from the boiler thus stop the hl stat from activating gerkros do have this issue seen a few if set above 65/70 trip the hl stat

    Kinda silly though. Wouldn't it cool all the rads And even the cylinder a little


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    you may well have a valid point but what kind of a temp drop are we looking at dtp


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    jimf wrote: »
    you may well have a valid point but what kind of a temp drop are we looking at dtp

    In the cylinder, no idea. In the rads shur they'd essentially drop down to whatever the stat is set to. In this case, 20 or 30


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    It doesnt make sense to me the way this boiler is wired.
    My opinion wound be.
    a/the switched live should turn on the boiler and pump
    b/The live feed through the pipe stat should also be wired to the pump also,similar to wiring a frost stat
    c/When switched live is turned off,the pump will run with the live feed from the pipe stat.
    d/This way if you set the pipe stat at 60 degrees, the pump will run for less and not cool down the heating system and still prevent the boiler from overheating
    Any thoughts..


  • Registered Users, Registered Users 2 Posts: 1,115 ✭✭✭wilser


    agusta wrote: »
    It doesnt make sense to me the way this boiler is wired.
    My opinion wound be.
    a/the switched live should turn on the boiler and pump
    b/The live feed through the pipe stat should also be wired to the pump also,similar to wiring a frost stat
    c/When switched live is turned off,the pump will run with the live feed from the pipe stat.
    d/This way if you set the pipe stat at 60 degrees, the pump will run for less and not cool down the heating system and still prevent the boiler from overheating
    Any thoughts..

    When C happens won't the boiler be still firing as its linked to the pump?
    Think you have to have it set up with A or B but not both unless you use a relay


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    Yes Wilser you are correct on C,my mistake
    How about this then,
    Using pipe stat,
    a/ connect the pump live to com
    b/ connect the permanent live to no
    c/connect switched live to nc

    no = normally open.closed when hot
    nc=normally closed.closed when cold

    When pipe cold = feed is by switched live
    when the pipe heats the pipe stat switches to the permanent live to feed the pump.
    When the boiler is turned off [switched live],the pump feed is by the permanent live until the temperature drops.


  • Registered Users, Registered Users 2 Posts: 1,115 ✭✭✭wilser


    What happens if you set the pipe stat to 50? If the pump starts when the pipe reaches 50 would that not work better as the rads won't be cooled too much?
    Looks like you may be over complicating things


  • Advertisement
  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    wilser wrote: »
    What happens if you set the pipe stat to 50? If the pump starts when the pipe reaches 50 would that not work better as the rads won't be cooled too much?
    Looks like you may be over complicating things
    Simplified it...
    if pipe stat set at 50 degrees, the switched live feed the pump until the pipe stat reaches 50 degrees


Advertisement