oil burner not working

  • 03-11-2014 7:19pm
    #1
    Registered Users, Registered Users 2 Posts: 310 ✭✭


    Need some help oil burner is acting srange it comes on rads heat up and burner turns off and won't come back on till system has gone cold it gets to first stage but won't fire up ?


Comments

  • Registered Users, Registered Users 2 Posts: 445 ✭✭Froststop


    stoeger wrote: »
    Need some help oil burner is acting srange it comes on rads heat up and burner turns off and won't come back on till system has gone cold it gets to first stage but won't fire up ?

    Is it a SuperQ by any chance?
    Had a similar problem with one last week.

    Is it getting very hot?
    Check your stat first.


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    stoeger wrote: »
    Need some help oil burner is acting srange it comes on rads heat up and burner turns off and won't come back on till system has gone cold it gets to first stage but won't fire up ?
    Could you explain what you mean "the burner gets to first stage"?


  • Registered Users, Registered Users 2 Posts: 310 ✭✭stoeger


    Froststop wrote: »
    Is it a SuperQ by any chance?
    Had a similar problem with one last week.

    Is it getting very hot?
    Check your stat first.

    Stat seems fine its an RBD burner i removed all the housing from around the burner and it was working as normal for an hour when i put housing back on it played up again


  • Registered Users, Registered Users 2 Posts: 310 ✭✭stoeger


    agusta wrote: »
    Could you explain what you mean "the burner gets to first stage"?

    Do you no when you first turn it on it hums before it fires up


  • Registered Users, Registered Users 2 Posts: 310 ✭✭stoeger


    agusta wrote: »
    Could you explain what you mean "the burner gets to first stage"?

    Do you no when you first turn it on it hums before it fires up


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 445 ✭✭Froststop


    stoeger wrote: »
    Stat seems fine its an RBD burner i removed all the housing from around the burner and it was working as normal for an hour when i put housing back on it played up again

    Run it without the housing, allow it switch off on temp and see with it start up on stat. If it dose not then you could have an air flow problem.


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    No,the houseing makes no difference.when you hear the hum noise,does the motor not rotate either before its meant to fire..,Also you said the burner comes back on when the system is cold.Is this still the case or will the burner not start at all now?


  • Registered Users, Registered Users 2 Posts: 310 ✭✭stoeger


    Froststop wrote: »
    Run it without the housing, allow it switch off on temp and see with it start up on stat. If it dose not then you could have an air flow problem.

    Done that and its starts and stops on stat


  • Registered Users, Registered Users 2 Posts: 310 ✭✭stoeger


    agusta wrote: »
    No,the houseing makes no difference.when you hear the hum noise,does the motor not rotate either before its meant to fire..,Also you said the burner comes back on when the system is cold.Is this still the case or will the burner not start at all now?

    Still the case


  • Registered Users, Registered Users 2 Posts: 445 ✭✭Froststop


    stoeger wrote: »
    Done that and its starts and stops on stat

    So it only acts up when the housing is fitted, am I correct?
    Has it an oil operated air damper or manually set damper?


  • Advertisement
  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    There is no oil operated damper on an rdb burner..


  • Registered Users, Registered Users 2 Posts: 445 ✭✭Froststop


    Your right agusta, found this http://www.rielloburners.co.uk/lumo/upload_documents/riello_rdb34technicalmanual29025872.pdf

    If the motor is turning would he need to check if it's pumping oil?


  • Registered Users, Registered Users 2 Posts: 2,842 ✭✭✭Billy Bunting


    stoeger wrote: »
    it comes on rads heat up and burner turns off and won't come back on till system has gone cold it gets to first stage but won't fire up ?

    Does this burner lock out, does the reset button light up ? do you need to push a button ?


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    Froststop wrote: »
    Your right agusta, found this http://www.rielloburners.co.uk/lumo/upload_documents/riello_rdb34technicalmanual29025872.pdf

    If the motor is turning would he need to check if it's pumping oil?
    From reading between the lines the motor is not turning.but i could be wrong.its not clear from op


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    capacitor or fuel pump


  • Registered Users, Registered Users 2 Posts: 310 ✭✭stoeger


    Right lad thanks for all the reply friend of mine had a good look and very things working till it gets hot then suts down he checked all the volts from moter and the only thing that'd not working right is the solinode


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    thats grand.so the hum noise you were hearing was actually the motor running continous,which in this case if the boiler/burner was hot would point to a faulty solonoid.


  • Registered Users, Registered Users 2 Posts: 2,842 ✭✭✭Billy Bunting


    Constantly running RDB can be caused by bad photocell


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    I think in 5 years I have only come across about 2 coil problems in rdb burners now p cell are another story


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    Constantly running RDB can be caused by bad photocell
    I agree,except in this case i didnt know the motor was running continous.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    my pick up on the post was the same as you agusta


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    Was a poorly described problem at times. Billy's last question (not last post), had it been answered, would have helped with pinning down the problem to a few components.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 2,842 ✭✭✭Billy Bunting


    agusta wrote: »
    I agree,except in this case i didnt know the motor was running continous.

    I agree with you, the OP didn't make it clear if the burner was locking out, but I didn't pick up that it was, so I presumed it wasn't.
    In most cases, capacitor, pump, solenoid, burner will lock out, Photocell no.