DB in kitchen cabinet?

  • 29-05-2014 9:14pm
    #1
    Registered Users, Registered Users 2 Posts: 707 ✭✭✭


    Anyone know if there are any regs relating specifically to the above? Providing its within the correct height limit.


Comments

  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    not allowed I'd say

    that would be considered a storage cupboard I think

    which isn't allowed


  • Registered Users, Registered Users 2 Posts: 707 ✭✭✭jeepers101


    Any specific regs you can guide me to? What I have in mind will be a cabinet dedicated to the board. It won't be used as storage.


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    it's in the rules section on distribution boards

    storage or airing cupboards I think it says


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    Maybe a kitchen cabinet was built around the DB that was not initially planned, often see this happen in utility rooms.
    If it is the case the cabinet maker should read up on the building regs as there are alot of regs in around the kitchen which certain appliances minimum distance etc. I dont think the DB should be removed if this is the case and wrong to be saying that it is installed incorrectly too.


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    I would think you could argue the case

    if it's a dedicated cupboard space


  • Advertisement
  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    I would think you could argue the case

    if it's a dedicated cupboard space

    It depends on the op, if the cupboard was an after thought i.e the home owner didnt like looking at the fuseboard and decided to put in a unit to cover it there is no arguing in that case.


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    It depends on the op, if the cupboard was an after thought i.e the home owner didnt like looking at the fuseboard and decided to put in a unit to cover it there is no arguing in that case.
    no arguing with what?

    if it's in a storage or airing cupboard it doesn't comply, doesn't matter which came first

    not saying that's the case here
    I think you can argue it's a dedicated space


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    if it's in a storage or airing cupboard it doesn't comply, doesn't matter which came first

    If for example the DB was in a utility and at the initial first fix it was agreed location of DB and house completed etc. 5 years down the line and a new family needing more storage so they decide to build cupboards along the wall where the DB is.
    Are you telling me that the electrician was wrong here?


  • Registered Users, Registered Users 2 Posts: 707 ✭✭✭jeepers101


    Thanks lads, seems a bit subjective imo. A cupboard is only a storage cupboard if its used for storage.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    if it's in a storage or airing cupboard it doesn't comply, doesn't matter which came first


    Exactly.

    If for example the DB was in a utility and at the initial first fix it was agreed location of DB and house completed etc. 5 years down the line and a new family needing more storage so they decide to build cupboards along the wall where the DB is.


    Then they the installation no longer complies with the regulations.
    The same logic would apply if the utility was turned into a shower room.

    Are you telling me that the electrician was wrong here?


    Who is right or wrong is not relevant.
    Apart from the fact that it is against the regulations the DB is unlikely to be as accessible, it may accidently become covered with items being stored in the cupboard which could contribute to it overheating and becoming a fire hazard.
    In short, this is simply not a good idea.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 378 ✭✭frankmul


    jeepers101 wrote: »
    Thanks lads, seems a bit subjective imo. A cupboard is only a storage cupboard if its used for storage.

    I agree with 2011. We all know that if something is built around a DB and there is storage space in it, it will eventually be used for storage


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    I think you could prob argue the case with an inspector if it happened by accident on a new job

    if the door was labelled

    DISTRIBUTION BOARD
    NOT TO BE USED FOR STORAGE

    you might get away with it

    but you wouldn't put it there by design as the OP proposes


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    I think you could prob argue the case with an inspector if it happened by accident on a new job

    if the door was labelled

    DISTRIBUTION BOARD
    NOT TO BE USED FOR STORAGE

    you might get away with it

    but you wouldn't put it there by design as the OP proposes


    Forget the inspector and apply common sense.
    This is not a good idea period!


  • Registered Users, Registered Users 2 Posts: 707 ✭✭✭jeepers101


    2011 wrote: »
    Forget the inspector and apply common sense.
    This is not a good idea period!

    Point taken


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    2011 wrote: »
    Then they the installation no longer complies with the regulations.

    Right, so now we have a non compliant installation thanks to the home owner watching too much Grand Designs and a trip to Ikea thus building the press.
    What do we do now to get it compliant?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Right, so now we have a non compliant installation thanks to the home owner watching too much Grand Designs and a trip to Ikea thus building the press.
    What do we do now to get it compliant?

    There are 2 options available:
    1) move the DB out of the cupboard
    2) remove the cupboard from around the DB

    It is not the purpose of the regulations (ET101) to offer practical solutions to unsafe practices.


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    Right, so now we have a non compliant installation thanks to the home owner watching too much Grand Designs and a trip to Ikea thus building the press.
    What do we do now to get it compliant?

    it will be the homeowners problem if he encloses the DB at a later stage.. he will have to pay for relocation if it's a problem on a periodic inspection or the like

    on a new installation it will be a problem for the REC as he can't sign off and may be partly/wholly to blame depending on the circumstances

    I still think you "might" be able to argue that it complies if the door was labelled etc..assuming it happens accidentally


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    I still think you "might" be able to argue that it complies if the door was labelled etc..assuming it happens accidentally

    What do you base this assumption on ?
    It is clearly not permitted.

    Your assumption is based on everyone being able to read, understand English, the notice never being removed, the notice being obeyed and an acceptance of a clear breach of regulations following an investigation if the DB went on fire.


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    2011 wrote: »
    What do you base this assumption on ?
    It is clearly not permitted.

    Your assumption is based on everyone being able to read, understand English, the notice never being removed, the notice being obeyed and an acceptance of a clear breach of regulations following an investigation if the DB went on fire.

    you may be right

    i am merely trying to play the devils advocate


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    2011 wrote: »
    There are 2 options available:
    1) move the DB out of the cupboard
    2) remove the cupboard from around the DB

    Option 2 would be my choice.
    2011 wrote: »
    Your assumption is based on everyone being able to read, understand English, the notice never being removed, the notice being obeyed and an acceptance of a clear breach of regulations following an investigation if the DB went on fire.

    Interesting point you brought up there, say if a DB cought fire due to a cupboard around it, insurance assessor comes in and sees the damage and states the cause of it, home owners insurance wont cover insurance so they go claiming off electrician would this be fair as the cabinet maker was the one who put it there.


  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    say if a DB cought fire due to a cupboard around it, insurance assessor comes in and sees the damage and states the cause of it, home owners insurance wont cover insurance so they go claiming off electrician would this be fair as the cabinet maker was the one who put it there.

    So in your hypothetical scenario, an electrician completes an electrical installation which complies fully with the regulations, following this the cupboard is built around the board? I don't think that any sane person could hold the electrician responsible for a third party building a cupboard that causes the installation to cease being the wiring regulations.

    If the electrician installed the DB properly it should not go on fire in the first place. Theoretically if the cupboard was full of clothes that were packed tightly around the DB they could be a contributing factor, but there would have to be some sort of a fault in the first place.


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    2011 wrote: »
    So in your hypothetical scenario, an electrician completes an electrical installation which complies fully with the regulations, following this the cupboard is built around the board? I don't think that any sane person could hold the electrician responsible for a third party building a cupboard that causes the installation to cease being the wiring regulations.

    I have the same opinion as you on that, kitchen fitters, carpenters should be more educated as I posted earlier in this thread, I must run through the building regs to see is there any regs on it.
    Theoretically if the cupboard was full of clothes that were packed tightly around the DB they could be a contributing factor, but there would have to be some sort of a fault in the first place.

    If clothes were packed tight like you say and heat generated off a bell trafo, mcbs on the limit the risk of fire would be a real presence and no fault.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    If clothes were packed tight like you say and heat generated off a bell trafo, mcbs on the limit the risk of fire would be a real presence and no fault.

    I am saying that although I certainly would not recommend doing anything that would make it harder for for a distribution board to cool I do not believe that this alone would cause a fire.


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    Some type bell trafos do get very hot though.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Some type bell trafos do get very hot though.

    If there was a real danger of a properly installed bell transformer overheating I would expect some sort of warning on the accompanying documentation.
    I would not use a bell transformer that is normally hot.


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    2011 wrote: »
    If there was a real danger of a properly installed bell transformer overheating I would expect some sort of warning on the accompanying documentation.

    Alot of trafos dont come with any paperwork or packaging so on that there must not be.
    I would not use a bell transformer that is normally hot.

    I have yet to install a type that don't run hot.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Alot of trafos dont come with any paperwork or packaging so on that there must not be.

    Well once it is CE marked and there are no special installation instructions then I would not expect it to go on fire to easily. The same can not be said for certain grid dimmer switches that come with explicit warnings about spacing etc..
    I have yet to install a type that don't run hot.

    Well I jest checked mine, it is warm and definitely not "very hot" and it isn't anything fancy :)


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    If clothes were packed tight like you say and heat generated off a bell trafo, mcbs on the limit the risk of fire would be a real presence and no fault.

    I don't think that's realistic myself.


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    Bruthal wrote: »
    I don't think that's realistic myself.

    It could contribute to a fire hazzard though would you agree?


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    It could contribute to a fire hazzard though would you agree?

    They will contribute to fueling a fire once started, but not to the risk due to causing DB components overheating.

    Just the same as furniture will fuel a fire, rather than causing one.


  • Closed Accounts Posts: 6,720 ✭✭✭Sir Arthur Daley


    Bruthal wrote: »
    They will contribute to fueling a fire once started, but not to the risk due to causing DB components overheating.

    I probably over thinking it, wouldnt the clothes tightly packed in front of a db act as an insulator and not allow the bell trafo or other components dissipate its heat?


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    I probably over thinking it, wouldnt the clothes tightly packed in front of a db act as an insulator and not allow the bell trafo or other components dissipate its heat?

    They would if there was enough heat to dissipate such that the temperature of the items rise to high enough level to cause a fire.

    Temperature rise in any item occurs until the heat dissipated away from it = heat input to it. A bell transformer would want to be almost glowing before it would cause a fire. Id say it could be encased in any material, and still wouldnt overheat.

    Its a bad idea alright to pack clothes against a DB. But I couldnt see it directly causing a fire, only contributing to one ignited by a problem in the board.