    Hi .Last month Ive got brand new Vokera LPG boiler fitted.All was fine until last week and it did not fire up on time and red light flashing.After reading manual it means that boiler needs be restarted.Fine,I did it and 2 days later same problem.There is no leaks and pressure is steady at 1.2-1.4 Bar.

    I will call service 2moro anyway but if some maybe have DIY will be great ;)


Comments

  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Hi .Last month Ive got brand new Vokera LPG boiler fitted.All was fine until last week and it did not fire up on time and red light flashing.After reading manual it means that boiler needs be restarted.Fine,I did it and 2 days later same problem.There is no leaks and pressure is steady at 1.2-1.4 Bar.

    I will call service 2moro anyway but if some maybe have DIY will be great ;)
    Could be lots of causes. What model boiler?
    Do you have a commissioning print out for the combustion?
    Basic question, but I have come across many not converted or not converted properly to run on LPG.


  • Registered Users, Registered Users 2 Posts: 844 ✭✭✭bigboss1986


    It is Vokera Rain 24 bi.
    He gave me some print out from some kind of tester but I can not find it.Also as far I remember he had to converted to LPG.
    I dont really know much about heating.
    If I find this print out what should I check?


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    I'd like the CO2 reading & the CO reading.


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Why did you have a standard efficiency boiler installed instead of a high efficiency one???
    Doesn't make sense for running costs & performance reasons.


  • Registered Users, Registered Users 2 Posts: 844 ✭✭✭bigboss1986


    shane0007 wrote: »
    Why did you have a standard efficiency boiler installed instead of a high efficiency one???
    Doesn't make sense for running costs & performance reasons.

    This is question to my Landlord :mad: It is still much better than old one.Once I find print out I will post here


  • Advertisement
  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Ok.
    Is the boiler outside?


  • Registered Users, Registered Users 2 Posts: 844 ✭✭✭bigboss1986


    Yes it is outside in lockup.


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    What was the fault light, green, yellow or red, flashing or solid?


  • Registered Users, Registered Users 2 Posts: 844 ✭✭✭bigboss1986


    Red flashing


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    If flashing, I would need the print out readings to ensure the combustion was correct.

    Do you have gas in the tank, i.e. Gas cooker is functioning if fitted?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 844 ✭✭✭bigboss1986


    I live in estate where LPG tank is in the middle of estate and then delivered to houses.It is only for central heating and nothing else (thanks god :D ) Im looking for this printout now so let u know asap


  • Registered Users, Registered Users 2 Posts: 844 ✭✭✭bigboss1986


    shane0007 wrote: »
    I'd like the CO2 reading & the CO reading.


    O2 % 15.0
    CO ppm 20
    CO2 % 3.9

    LPG


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    O2 % 15.0
    CO ppm 20
    CO2 % 3.9

    LPG

    TBH, it's either way off the scale or he printed those figures when the boiler was in low fire.
    If set up way under gassed on the burner pressure, this could account for lock out.

    I would be very suspect of the burner pressures set up on the boiler.

    Did you put through a service call?


  • Registered Users, Registered Users 2 Posts: 8,816 ✭✭✭Markcheese


    If it's a new boiler , ring the plumber who installed it quick ... If there's a quick fix he should sort it .. Or know to call vokera's service rep ...

    Slava ukraini 🇺🇦



  • Registered Users, Registered Users 2 Posts: 844 ✭✭✭bigboss1986


    shane0007 wrote: »
    TBH, it's either way off the scale or he printed those figures when the boiler was in low fire.
    If set up way under gassed on the burner pressure, this could account for lock out.

    I would be very suspect of the burner pressures set up on the boiler.

    Did you put through a service call?


    He is coming next week.Are those numbers are bad?Is there anything I should mention to service guy?


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    They are very low. If it's the Manufacturer's engineer calling, I wouldn't worry about it as he/she quickly determine the issue. Make sure you show them the print out.

    The CO2 figure is very low, more in the realms of low fire. When analyising, we set up boilers in both high & low fire, but figures to be inputted on Certs & analyiser print outs would always be in high fire (maximum gas output scenario conditions).

    If the installer has the boiler running in high fire with such low figures, the boiler would struggle to run properly every time it goes into high fire.

    It is especially important to set up LPG as per MI's as there is 2.5 times more bang (energy) in LPG over natural gas.