Power problem in new house

  • 22-01-2014 5:14pm
    #1
    Registered Users, Registered Users 2 Posts: 470 ✭✭


    Bulbs are constantly blowing, the TV flicks on and off sometimes and the main 63A mcb trips every few days. The ESB have come out and measured the voltage at the meter over one week and say it's fine.
    The Voltage seems to be a constant 235v at the meter and the same at any outlet inside the house.

    A loop reading at the meter gives me 1.8ohms. This is higher than normal but it's hardly the reason for the problems is it?


Comments

  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    tn-c-s should be about 0.35 ohm maximum at the supply if i recall...you're Zl readings must be way over at 'final circuits' if that's the case

    it sounds like maybe there a supply problem with a bad connection or volt drop on the supply lines on the network etc. going by what you're saying...what's the volt drop like with a heavy load

    is everything ok at the distribution board and all connections tight


  • Registered Users, Registered Users 2 Posts: 2,630 ✭✭✭Zen65


    17larsson wrote: »
    A loop reading at the meter gives me 1.8ohms. This is higher than normal but it's hardly the reason for the problems is it?

    How are you measuring the loop impedance?


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    Zen65 wrote: »
    How are you measuring the loop impedance?

    something not right

    is this the 'main ocpd'(63amp mcb) in the cabinet that's tripping i wonder


    i'd be checking connections at mcb and distribution board anyhow

    or is there overload condition or disturbing loads present tripping 63amp mcb if ESBN have recorded voltage and found no issues


  • Registered Users, Registered Users 2 Posts: 470 ✭✭17larsson


    tn-c-s should be about 0.35 ohm maximum at the supply if i recall...you're Zl readings must be way over at 'final circuits' if that's the case

    it sounds like maybe there a supply problem with a bad connection or volt drop on the supply lines on the network etc. going by what you're saying...what's the volt drop like with a heavy load

    is everything ok at the distribution board and all connections tight

    Yeah the readings inside are high as 2.8ohms. I've seen a few houses with a supply impedance of 0.5 or 0.6 but never as high 1.8 so that's why I just thought there might be a link between that and the problems they are having. I might stick an ammeter on and see if there any funny readings. All connections are tight


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    yes

    if it's actually 1.8 at the supply you will need to contact esbn

    but that should have showed up as an issue on a voltage recorder unless it's a problem with the short neutralizing
    section at the cabinet


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 470 ✭✭17larsson


    I would have thought the ESB would have noticed the high impedance when they were testing the voltage but maybe not. I must ask the spark that originally wired the house if he got those readings when he tested the house initially. Yeah it could be a loose neutralizing connection under the seal. I will talk to the original spark tomorrow and see if I can get any more info