Grant indoor boiler

  • 03-01-2014 7:17pm
    #1
    Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭


    A customer rang me today saying her boiler would heat the rads and once up to temperature it seems the rads start to cool down but she says the boiler is still going but sounds like it not firing. Why isn't it going to lockout?


Comments

  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Dtp1979 wrote: »
    A customer rang me today saying her boiler would heat the rads and once up to temperature it seems the rads start to cool down but she says the boiler is still going but sounds like it not firing. Why isn't it going to lockout?

    You really need to be in front of it to see what it is doing.


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    shane0007 wrote: »
    You really need to be in front of it to see what it is doing.

    I know ye was just hoping it sounded familiar to somebody. I've never came across a burner where the fan ran continuously. I'm assuming dodgy photocell or control box


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    If it's heating the rads, it's firing.
    If it's running & running without firing & not going to lock out, it could be photocell, solenoid coil, control box or incorrect return voltage (50v +/-3) back from the motor.


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    Dtp1979 wrote: »
    A customer rang me today saying her boiler would heat the rads and once up to temperature it seems the rads start to cool down but she says the boiler is still going but sounds like it not firing. Why isn't it going to lockout?

    dtp you seem to get all the easy ones


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    shane0007 wrote: »
    If it's heating the rads, it's firing.
    If it's running & running without firing & not going to lock out, it could be photocell, solenoid coil, control box or incorrect return voltage (50v +/-3) back from the motor.

    I wonder is it going through the first cycle ok from cold and then failing to ignite when hot

    something not adding up here


  • Advertisement
  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    Would do that on a faulty PE cell, or a solenoid as it heats up and goes open circuit (as per Shanes post above)


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    jimf wrote: »
    I wonder is it going through the first cycle ok from cold and then failing to ignite when hot

    something not adding up here

    Ye I know!! Lookin forward to going to it (sarcasm) :)


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    I would go with shane and dgobs suggestion first p cell is the usual culpit ive often seen them faulty and motor running constantly

    but ive never seen 1 go faulty mid cycle without lockout


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    heres a chance for another question lads sorry dtp

    what happens is the p cell seeing false light or what thus thinking burner is lgnited and goes no further with the start sequence


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    jimf wrote: »
    heres a chance for another question lads sorry dtp

    what happens is the p cell seeing false light or what thus thinking burner is lgnited and goes no further with the start sequence

    Photocell sees what it sees. The control box interprets the lux of the photocell as resistance. During it's 12 sec purge, if it sees light, the CB will go immediately to lock out as it only wants to see darkness.
    If after the ignition period, it wants to see light, i.e. a flame but if the flame is too bright or too dim, the resistance will not be within the parameters the CB wants to see & will also go to lock out.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    shane0007 wrote: »
    Photocell sees what it sees. The control box interprets the lux of the photocell as resistance. During it's 12 sec purge, if it sees light, the CB will go immediately to lock out as it only wants to see darkness.
    If after the ignition period, it wants to see light, i.e. a flame but if the flame is too bright or too dim, the resistance will not be within the parameters the CB wants to see & will also go to lock out.

    so this would explain when you disconnect the faulty p cell from the cb it then ignites and goes to lock out


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    jimf wrote: »
    so this would explain when you disconnect the faulty p cell from the cb it then ignites and goes to lock out

    Absolutely.
    If you are getting a continuous running without firing, disconnect the photocell & if it goes to lock out, the photocell is 100% the issue. If it continues to run, next test the resistance of the solenoid coil, etc.


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    shane0007 wrote: »
    Absolutely.
    If you are getting a continuous running without firing, disconnect the photocell & if it goes to lock out, the photocell is 100% the issue. If it continues to run, next test the resistance of the solenoid coil, etc.

    in 4 years ive never had a faulty coil on an rdb am I just lucky

    plenty of gammy p cells with issues as discussed above


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    jimf wrote: »
    in 4 years ive never had a faulty coil on an rdb am I just lucky

    plenty of gammy p cells with issues as discussed above

    I've replaced a few but not on a regular basis, perhaps a couple per year.


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    My thinking would be if the photocell was faulty,ie, see light, which is giving back lower resistance than the parameter it should be to the control box.The burner will not go to lock out.It will run continuous.By disconnecting photocell from control box the control box only sees darkness[high resistance],so the burner will start and then go to lock out because it dosent see light on ignition.Is this not correct..


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    shane0007 wrote: »
    I've replaced a few but not on a regular basis, perhaps a couple per year.

    and you would be seeing a lot more burners than me so not a big consumable
    part then


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    agusta wrote: »
    My thinking would be if the photocell was faulty,ie, see light, which is giving back lower resistance than the parameter it should be to the control box.The burner will not go to lock out.It will run continuous.By disconnecting photocell from control box the control box only sees darkness[high resistance],so the burner will start and then go to lock out because it dosent see light on ignition.Is this not correct..
    Other way around. No light = no resistance. Light will increase the resistance.
    If CB doesn't receive back a reading within its parameter, it doesn't know if there is a flame or not. So it takes no chance & runs fan continuously.


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    did you get to this yet dtp


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    jimf wrote: »
    did you get to this yet dtp

    Funny u should ask Jim cause I'm just in from it. When I got there burner was goin flat out but not firing. Turned it off and on a few times and same. Changed photocell and away it went! Thanks again to all who helped


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    glad to hear that

    thanks for letting us know the outcome


  • Advertisement
  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Dtp1979 wrote: »
    Funny u should ask Jim cause I'm just in from it. When I got there burner was goin flat out but not firing. Turned it off and on a few times and same. Changed photocell and away it went! Thanks again to all who helped

    Just remember the simple test to do before changing. Just disconnect the photocell lead from the CB & if it goes to lock out, the photocell is the issue. Saves messing about with new one if another component is at fault.


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    shane0007 wrote: »
    Just remember the simple test to do before changing. Just disconnect the photocell lead from the CB & if it goes to lock out, the photocell is the issue. Saves messing about with new one if another component is at fault.

    No lead on this photocell but I know what ya mean Shane!


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Dtp1979 wrote: »
    No lead on this photocell but I know what ya mean Shane!

    What burner was it?


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    shane0007 wrote: »
    What burner was it?

    G3
    And yes I'm well aware of the air issue too as I had to inform the customer today


  • Registered Users, Registered Users 2 Posts: 800 ✭✭✭esox28


    What's the air issue if you don't mind me asking?

    Great posts on pcell lads.


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Dtp1979 wrote: »
    G3
    And yes I'm well aware of the air issue too as I had to inform the customer today

    G3, just remove the photocell & click back on the control box.


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    esox28 wrote: »
    What's the air issue if you don't mind me asking?

    Great posts on pcell lads.

    On the indoor boiler it's not a balanced flue that I have. So basically the burner is taking the air from whatever is inside the casing


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Dtp1979 wrote: »
    On the indoor boiler it's not a balanced flue that I have. So basically the burner is taking the air from whatever is inside the casing

    What model Grant is it?
    Boiler casings are designed to take air for combustion from the room it's in as long as there is a suitably sized non-closable vent in the room, it should be fine.


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    shane0007 wrote: »
    What model Grant is it?
    Boiler casings are designed to take air for combustion from the room it's in as long as there is a suitably sized non-closable vent in the room, it should be fine.

    'Twas the grant multipass Shane


  • Advertisement
  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Dtp1979 wrote: »
    'Twas the grant multipass Shane

    What is your concern with it? The indoor casings are vented to the room.


  • Registered Users, Registered Users 2 Posts: 12,870 ✭✭✭✭Dtp1979


    shane0007 wrote: »
    What is your concern with it? The indoor casings are vented to the room.

    The only holes I saw Shane were the ones for the wires. Plus there isn't a vent in the room itself


  • Closed Accounts Posts: 4,677 ✭✭✭shane0007


    Dtp1979 wrote: »
    The only holes I saw Shane were the ones for the wires. Plus there isn't a vent in the room itself

    The casing are designed to be able to intake sufficient at inducing air for combustion under extreme conditions, i.e. burning gas oil at highest boiler output with full air intake open.

    My only concern would be an open flue appliance with no room fixed vent. For adventitious air, you can disregard the first 5kw if the boiler is pre, I think 2006 or 2003. I usually disregard adventitious air due to future proofing of houses.