Plumbing and heating

  • 13-10-2013 8:20am
    #1
    Registered Users, Registered Users 2 Posts: 39


    Opinions please .. I have a viessmann condenser boiler for 4 years now and during the week I noticed the pressure dropping on gauge and water running out of pipe at side of house while heating on.. I got a rgi gas/servicean out to look at it yesterday .. He serviced the boiler and put a new safety value on the boiler to solve the problem .. Unfortunately we are no further on this morn .. It's so annoying .. I had to open value in hot press for a few mins to put some pressure back in the system .. Anyone any idea what it could be ??


Comments

  • Technology & Internet Moderators Posts: 28,830 Mod ✭✭✭✭oscarBravo


    Moved from Open Source.


  • Registered Users, Registered Users 2 Posts: 21 mollybelle


    Hi, I have just had a Boru 600i installed and the glass door has blackened the first time I used it, any advice on how to use the dampers properly so as to stop this happening would be very much appreciated.

    Thanks in advance.


  • Registered Users, Registered Users 2 Posts: 2,409 ✭✭✭sullzz


    mollybelle wrote: »
    Hi, I have just had a Boru 600i installed and the glass door has blackened the first time I used it, any advice on how to use the dampers properly so as to stop this happening would be very much appreciated.

    Thanks in advance.

    Is think you should start your own thread , you might get a reply instead of hijacking someone else's.

    OP your plumber should have either depressurised your expansion vessel or replaced it , the safety valve was letting water through for a reason.


  • Registered Users, Registered Users 2 Posts: 8,565 ✭✭✭K.Flyer


    The OP's problem was resolved a couple of weeks ago on a different thread.
    cupcakes15 wrote: »
    all sorted...it was an expansion prob seemingly ...got ur man back again...flip it i thought why get anyone else after paying him good money