Back boiler air lock

  • 11-09-2013 8:39pm
    #1
    Registered Users, Registered Users 2 Posts: 406 ✭✭


    Just a bit of advice needed on how to get rid of an air block in a solid fuel back boiler, was running perfect back in April, lit the fire last night and it just hissed and banged all night and barely heated the rads, spent the day bleeding a the rads , it's still banging, not as bad but l can still hear some air in it, it's not a complicated system and had just one circulation pump on the system which I changed a few yrs ago..


Comments

  • Registered Users, Registered Users 2 Posts: 1,884 ✭✭✭Robbie.G


    denlaw wrote: »
    Just a bit of advice needed on how to get rid of an air block in a solid fuel back boiler, was running perfect back in April, lit the fire last night and it just hissed and banged all night and barely heated the rads, spent the day bleeding a the rads , it's still banging, not as bad but l can still hear some air in it, it's not a complicated system and had just one circulation pump on the system which I changed a few yrs ago..

    It sounds like you have a problem with circulating pump or stat.
    What way do you switch your pump on is it on a switch or a pipe stat and comes on automatically


  • Registered Users, Registered Users 2 Posts: 406 ✭✭denlaw


    Robbie.G wrote: »
    It sounds like you have a problem with circulating pump or stat.
    What way do you switch your pump on is it on a switch or a pipe stat and comes on automatically

    It's a stat on a pipe which comes on automatically, I changed the stat last yr ..


  • Registered Users, Registered Users 2 Posts: 1,884 ✭✭✭Robbie.G


    denlaw wrote: »
    It's a stat on a pipe which comes on automatically, I changed the stat last yr ..

    Make sure your stat is operating the pump or pump is possibly jammed


  • Registered Users, Registered Users 2 Posts: 406 ✭✭denlaw


    Robbie.G wrote: »
    Make sure your stat is operating the pump or pump is possibly jammed

    Just checked it, pump seems fine, not jammed but very hot .
    Havnt touched the stat since last yr


  • Closed Accounts Posts: 2,097 ✭✭✭Dtp79


    Solid fuel done properly shouldn't airlock as it rises to the cylinder then to the vent. Check there is water in your small tank in your attic


  • Advertisement
  • Moderators, Regional North West Moderators Posts: 19,158 Mod ✭✭✭✭byte
    byte


    Robbie.G wrote: »
    Make sure your stat is operating the pump or pump is possibly jammed
    Funny, this happened the pump for my oil heating at the end of last year when it wasn't used for some months. It hummed like it was working, yet was very hot but not circulating water beyond the closest rad. This in turn caused the oil boiler to cut out (back boilers of course can't do this). Hit it a small smack with a hammer and suddenly the hum slightly changed in tone, and you could hear water gurgling.

    Problem fixed :)


  • Registered Users, Registered Users 2 Posts: 1,884 ✭✭✭Robbie.G


    denlaw wrote: »
    Just checked it, pump seems fine, not jammed but very hot .
    Havnt touched the stat since last yr

    Did you screw off the front bleed screw and check that the pump was turning.As Dtp said check header tank for water


  • Registered Users, Registered Users 2 Posts: 406 ✭✭denlaw


    Update, tank up in attic was empty as suggested, ballcock stuck, one more thing, I presume I'll have to bleed ALL the rads ..right?

    Thanks again lads, if I can be of any help pc/laptop tablet networking trouble shooting wise, give me a pm ..whst goes round comes round as me ma used to say ..