IR reading t&e coil

  • 16-10-2012 2:48pm
    #1
    Closed Accounts Posts: 4,431 ✭✭✭


    what's an acceptable reading between lives joined and cpc on 100m coil 1.5t+e?

    i was measuring 300M ohm on a coil today-seems a bit low?


Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    300,000,000 ohms is pretty high
    I would be happy enough with that if I were you:)


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    2011 wrote: »
    300,000,000 ohms is pretty high
    I would be happy enough with that if I were you:)
    i don't normally check them
    it's prob acceptable


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    M cebee wrote: »
    i don't normally check them
    it's prob acceptable

    Definitely.
    Out of interest, what voltage did you meggar them at?


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    1000v


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    M cebee wrote: »
    1000v
    I would imagine that if you tested it at 500V or 230VAC the meter would read infinity.

    Either way you are well covered.


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Likely be a higher reading if you roll it out as well. 300 meg is fine.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    2011 wrote: »
    I would imagine that if you tested it at 500V or 230VAC the meter would read infinity.

    Either way you are well covered.
    250v
    i doubt it on the one i was using
    it goes way up
    i was reading 4000 megohm on 2.5 t+e

    thats what had me curious

    i think the other one which is in for calibration shows infinity at a much lower
    IR reading