Immersion flex?

  • 02-10-2012 12:21pm
    #1
    Registered Users, Registered Users 2 Posts: 105 ✭✭


    Hi.
    What size flex is used between the immersion switch and the immersion itself?

    Also what's used for circulation pumps etc. in a hot press?

    Thanks.


Comments

  • Posts: 0 [Deleted User]


    5 x 2.5 for immersion flex. 3 x 1.5 for pumps. All heat resistant flex


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    i think the immersion is normally supplied with 4 by 1.5 HR flex

    no harm to use 2.5 anyhow


  • Posts: 0 [Deleted User]


    Sorry I actually meant 4 x 2.5 for the immersion


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    M cebee wrote: »
    i think the immersion is normally supplied with 4 by 1.5 HR flex

    Yes, you are correct.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    2011 wrote: »
    Yes, you are correct.

    yes the 2.5 is a bit big-afaik the 1.5 is rated for the 3kw load which would be the determining factor here rather than the breaker size


  • Advertisement
  • Closed Accounts Posts: 517 ✭✭✭JOHNPT


    A Whirlpool Hob is rated at approx 5.5kw - what size flex can be used to connect these to junction box?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    3 x 4sq. heat resistant flex would be suitable.


  • Registered Users, Registered Users 2 Posts: 105 ✭✭LostInLM


    Thanks. 4x1.5 HR will do it so.