Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Under sink water heater Rcd?

  • 23-06-2012 9:54am
    #1
    Registered Users, Registered Users 2 Posts: 55 ✭✭


    Well this is my first time posting a question and things seem to be a bit quiet here :D. Anyway i'm trying to find out what is causing the rcd to trip in a kitchen of a small restaurant. They have two 2kw under sink water heaters on the same circuit in staff and customer toilets. The previous sparks disconnected them so i have the task of getting them going again. I belled both heaters out and found that resistance was good on both,the earth was clean and they both heat up grand but once in a while the rcd trips. Is it still possible that one or both of these is at fault due to a slightly split element or something? These are approx 8 years old too and would be on 24hrs a day. Thanks :)


Comments

  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    if the IR readings are good, they wont trip an rcd

    - unless there's a fault on the final circuit itself


  • Registered Users, Registered Users 2 Posts: 5,401 ✭✭✭DublinDilbert


    When you say you belled them, did you just do a continuity test or megger them?

    They must of been disconnected for a reason. If they are wired back to the board you could place them on thier own rcbo's, that would tell you quick enough.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    when you say you belled them out-are you using a multimeter?
    You'll need a megger.

    Is there a lot of appliances on the rcd?


  • Registered Users, Registered Users 2 Posts: 55 ✭✭desoc32


    Continuity test with my trusty fluke multimeter. I don't have any test equipment at the mo. I had run in a new supply from the board to the heaters as the old supply was disconnected somewhere by the last electrician. ( I'm the third electrician at this now!) I should also of mentioned that there is a double socket before the heaters which is where i fed into and made safe the old feed. This socket powers a microwave which for the last while was fed from an extension lead from another rcd'd circuit while it's own socket was off. Now i'd imagine the odd blender etc could be plugged into this socket too. I will put in an rcbo asap and see what happens. If you think meggering might help i'll borrow one from a mate.
    Had similar prob now that i think of it with an immersion element which was tripping rcd. Couldn't find the fault with power and resistance was good on element. Decided to change out the element anyway and was a slight split upon close inspection. New element worked grand :)


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    i would try to megger them and the final circuit if necessary before bothering with rcbo's

    -you should be able to check everything in one go at the DB if you can borrow a tester

    there's no diversity afaik on thermostatic water heating so you've 4kw +a 13amp socket if they're all on a 2.5 radial?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    if you ran in 2 circuits for the undersink heaters then i would put them on 2 rcbo devices
    is it possible that the original rcd is tripping on overload
    the 2 waterheaters together will draw 20-25amps
    are there any hand dryers etc on the rcd

    i would stick the clip on meter on the rcd to test the load


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    meercat wrote: »
    if you ran in 2 circuits for the undersink heaters then i would put them on 2 rcbo devices
    is it possible that the original rcd is tripping on overload
    the 2 waterheaters together will draw 20-25amps
    are there any hand dryers etc on the rcd

    i would stick the clip on meter on the rcd to test the load

    rcd doesn't trip on overload? do you mean mcb?


  • Registered Users, Registered Users 2 Posts: 55 ✭✭desoc32


    Ok they just tripped again :eek: so i'm gonna go there Monday and pull in a second cable for one of the heaters. Will also try borrow a megger just to see. So that's two new supplies out and i'll have them on seperate rcbos. Belt and braces here! If both heaters and microwave etc are on i suppose it could be using 5000w / 230v so 22amps or more. The hand dryers are on a seperate supply. Diversity definitely doesn't apply here but i think i was allowing myself some anyway as apparently they worked fine for years on old 2.5 supply. Will post back Monday.
    Thanks M Cebee and Meercat!


  • Registered Users, Registered Users 2 Posts: 55 ✭✭desoc32


    M cebee wrote: »
    rcd doesn't trip on overload? do you mean mcb?

    I was thinking that the mcb would be the one to go if overloaded at 20+amps or live fault etc but it's the rcd that's tripping which makes it more of an imbalance or leakage between live and neutral. Anyway best to have them on their own rcbo's and go from there


  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    M cebee wrote: »
    rcd doesn't trip on overload? do you mean mcb?

    i always assumed that once the load exceeded the rating of the rcd,it tripped
    remember having a 40amp rcd on a single row board that kept tripping intermittently
    replaced it with 63amp one and resolved the problem


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    desoc32 wrote: »
    I was thinking that the mcb would be the one to go if overloaded at 20+amps or live fault etc but it's the rcd that's tripping which makes it more of an imbalance or leakage between live and neutral. Anyway best to have them on their own rcbo's and go from there

    the mcb itself might not be overloaded
    the combined load of all the mcbs(water heating/hand dryers/pumps/kitchen equipment)may..... imho
    worth checking the load anyway while your at it


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    meercat wrote: »
    i always assumed that once the load exceeded the rating of the rcd,it tripped
    remember having a 40amp rcd on a single row board that kept tripping intermittently
    replaced it with 63amp one and resolved the problem

    no ,the 40 and 63amp is just the current rating


  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    M cebee wrote: »
    no ,the 40 and 63amp is just the current rating

    learning all the time;)


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    desoc32 wrote: »
    Ok they just tripped again :eek: so i'm gonna go there Monday and pull in a second cable for one of the heaters. Will also try borrow a megger just to see. So that's two new supplies out and i'll have them on seperate rcbos. Belt and braces here! If both heaters and microwave etc are on i suppose it could be using 5000w / 230v so 22amps or more. The hand dryers are on a seperate supply. Diversity definitely doesn't apply here but i think i was allowing myself some anyway as apparently they worked fine for years on old 2.5 supply. Will post back Monday.
    Thanks M Cebee and Meercat!

    check them first before you do any major work

    could be that the intermittent tripping is unrelated to the heaters


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    may be a problem somewhere else

    accumulated leakage-too many appliances and circuits maybe


    you can do the 250V IR test on the outgoing side of the rcd ,might show up a low reading?


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    meercat wrote: »
    learning all the time;)

    Indeed, m cebee is correct, an rcd wont trip on overload, unless any slight leakage is also increasing with the increased current. The rating is just what they can continuously carry.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    meercat wrote: »
    learning all the time;)
    Same as


Advertisement