help with boiler

  • 04-12-2011 7:15pm
    #1
    Registered Users, Registered Users 2 Posts: 2,352 ✭✭✭


    Hi folks. Little problem here. I have ThermTec Dual Immersion Heater, and it doesn't heat up when heating is on. i know, there is tap, if i am open it, then home heating system have heat up boiler. i know it was working in spring, and when warm weather came, i just closed that tap. now i opened it, but no sign of warm water any more. there is warm pipe water befor that tap, but cold after that. heating these days working quiet often, and no hot water in kitchen nor in bathroom.
    I can get hot water if i switch on electricity, but i wont use it as that boiler designed heat up from home heating system. ( i have gas heating).

    Any ideas where is problem ? Could be that tap broken ?

    In picture you can see that boiler, and red tap in bottom.

    04122011329.jpg

    Thanks


Comments

  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    the gate valve is probably seized and needs to be replaced
    have you tried turning it anti-clockwise
    sometimes turning it clockwise a fraction before anti-clockwise will help

    build up of hard water and lack of use will sometimes cause this
    is the valve rotating at all?


  • Registered Users, Registered Users 2 Posts: 2,842 ✭✭✭Billy Bunting


    It sounds like your talking about the red gate valve at the bottom of the cylinder?? if so, they are notorious for jamming in the off position, the fix is to replace it.


  • Registered Users, Registered Users 2 Posts: 2,352 ✭✭✭Mar4ix


    i think i fixed it, it was turning anticlockwise first time just one twist, and then i bit force it anticlockwise, and now it turning 10 times. i turn 10 times clockwise back, it stopped, then i turn it anticlockwise, again went one twist, then i again force anticlockwise and again 10 times turn anticlockwise until it stop. Hot water pass now that valve, and can feel warm water pass that valve. will see if ill see hot water in kitchen and bathroom. :)


  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    happy days


  • Registered Users, Registered Users 2 Posts: 2,352 ✭✭✭Mar4ix


    meercat wrote: »
    happy days


    still concerned about this, as itll be "happy days" when hot water in kitchen and bathroom taps. Let ya know how it goes. Any one knows how much time should take heating system heat up that boiler ?

    I am more mechanic, than plumber.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,352 ✭✭✭Mar4ix


    yeeeee.. happy days :)


  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat