Splitting Tails to Second CU

  • 30-11-2011 10:46am
    #1
    Registered Users, Registered Users 2 Posts: 5,401 ✭✭✭


    Hi all,

    Is there any regs covering where tails are split to supply a second consumer unit in a domestic installation? Both consumer units will be located pretty much side by side. Is it ok if each individual board has its own disconnect?

    Thanks


Comments

  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    Every db needs an isolating switch

    The only way you can add a second board
    is as a sub-board

    in other words you have to have 63amp main overcurrent protection unless you get an increase in capacity from esbn


  • Registered Users, Registered Users 2 Posts: 5,401 ✭✭✭DublinDilbert


    M cebee wrote: »
    Every db needs an isolating switch

    The only way you can add a second board
    is as a sub-board

    Thanks, this is what i was wondering. So is each DB allowed have its own isolating switch? or does there have to be one for the whole installation?


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    Every installation requires a main isolating switch-to cut power totally

    every distribution board requires an isolating switch(main switch) in the board


  • Registered Users, Registered Users 2 Posts: 5,401 ✭✭✭DublinDilbert


    M cebee wrote: »
    Every installation requires a main isolating switch-to cut power totally

    every distribution board requires an isolating switch(main switch) in the board

    Cool, that's pretty much what i thought.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    Basically you cant split tails coming in

    you can feed sub-board from the outgoing side of main isolating switch/ocpd or an mcb assuming theres capacity for any additional loads youre connecting


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,612 ✭✭✭Dardania


    what about if the main isolating device is the 63A MCB in the meter cabinet? Can two sub boards be run from it?


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    Dardania wrote: »
    what about if the main isolating device is the 63A MCB in the meter cabinet? Can two sub boards be run from it?

    i took it that the main ocpd was located indoors here and tails were being split before main ocpd

    with the new setup -it wouldn't be standard practice anyhow

    they'd have to be two separate buildings with no more than standard demand in total

    i would wire from main db as normal


  • Registered Users, Registered Users 2 Posts: 3,612 ✭✭✭Dardania


    M cebee wrote: »
    i took it that the main ocpd was located indoors here and tails were being split before main ocpd

    with the new setup -it wouldn't be standard practice anyhow

    they'd have to be two separate buildings with no more than standard demand in total

    i would wire from main db as normal

    I'd tend to agree with that you should extend from main db to the next, if nothing more to prevent the possibility of simultaneous peaks causing trips, and in case someone not in the know knocks off one board and thinks they've isolated the house when in fact they havent, but in principle theres nothing stopping you (from what I can see in the regs) in branching at the meter cab.

    If you really wanted to do it properly, surely you could fit a main MCB and two outgoing 40A MCBs in the weatherproof enclosure in the metering cab...


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    suppose you could do that providing the demand was such that the main ocpd isn't going to be overloaded regularly
    and one is an outbuilding


    reci/ecssa would likely pull you up on it as it's a distribution board in the cabinet


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    This is what would be normal in an industrial installation, and I would do the same in a domestic:


    ............................Meter cabinet
    ...................................⬇
    .......................Main distribution board
    .......................⬇..........................⬇
    ...........Sub Dist Board A................Sub Dist Board B





    The main distribution board would contain a main switch fuse as well as switch fuses for sub boards A & B.

    Sub boards A and B would not have main fuses, but main isolators instead.

    I seem to need the dots to get my arrows to align! Please ignore them :)