immersion

  • 22-09-2011 8:38pm
    #1
    Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭


    immersion not heating water but not tripping breaker,any thoughts?
    i am a sparks work in maintenance so have not done one in a long time,
    thanks guys!


Comments

  • Registered Users, Registered Users 2 Posts: 4,823 ✭✭✭meercat


    either the thermostat
    or the overheat has tripped
    or faulty timer
    or faulty immersion switch
    or burnt out connection
    or blown fuse/tripswitch
    or element gone(unlikely if nothing blown)


  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    thanks for speedy reply meercat,tested switch continuity all good there,no overheat on the stat so cant be that either!i just find it strange that if it is the element why its not tripping the breaker!!


  • Registered Users, Registered Users 2 Posts: 4,823 ✭✭✭meercat


    sometimes those overheat switches are un noticable
    how old is the immersion
    have you 230v to each element


  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    doesnt look to old mate had a good look around for the overheat and could not see one anywhere,i know on my one at home its quite noticeable!

    symptoms do seem to point to the overheat though any idea when they started putting them on the stat?


  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    sorry ye 230 goin to each element aswell mate!


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 4,823 ✭✭✭meercat


    4-5 years on some makes
    have you checked voltage to elements
    you hardly have a clip on amp meter to check loads


  • Registered Users, Registered Users 2 Posts: 4,823 ✭✭✭meercat


    any chance pic of stat


  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    unfortunately i cant get one at the moment as im just home from the house!in between the 2 terminals it looks like there was an overheat but it wasnt raised much so im pretty certain thats not it!
    no continuity through stat when immersion is off...correct?


  • Registered Users, Registered Users 2 Posts: 4,823 ✭✭✭meercat


    http://www.boards.ie/vbulletin/showthread.php?t=2056324283
    post 12 may help
    if not it may be on the stat itself


  • Registered Users, Registered Users 2 Posts: 4,823 ✭✭✭meercat


    no continuity through stat when immersion is off...correct?

    if there is no hot water in cylinder then there should be continuity through the stat


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,141 ✭✭✭maxamillius


    possible that i just missed it il have to have another look!

    tank water cold power off and no continuity through the stat!


  • Registered Users, Registered Users 2 Posts: 87 ✭✭PrismES


    possible that i just missed it il have to have another look!

    tank water cold power off and no continuity through the stat!
    Faulty Stat, stat should be closed


  • Registered Users, Registered Users 2 Posts: 68 ✭✭Dufftronic


    continuity is all well and good, but it's an ohmic value you want to see. At a guess you'd prob want to see about 40Ohms through the element.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Dufftronic wrote: »
    continuity is all well and good, but it's an ohmic value you want to see. At a guess you'd prob want to see about 40Ohms through the element.

    18 ohms through the bath element, 26 through the sink. They are roughly what to expect.

    Through the stat which is what was mentioned was missing should be 0 ohms.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    No its something like 19 and 25 for the 3 and 2kw