Systemlex

  • 09-09-2011 9:25am
    #1
    Registered Users, Registered Users 2 Posts: 12


    HI.
    I am currently installing a solid fuel stove into my home. The stove is plumbed in fine but i need to know how to wire in the stat and pump for stove into the System lex control panel. This is a second means of heating as there is a boiler outside too.


Comments

  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    shouldn't be much to it

    is the stove heating the water or what's the story

    when i looked at it a while back there was provision for 2 heat sources -unfortunately i can't recall exact details


  • Registered Users, Registered Users 2 Posts: 463 ✭✭grousedogtom


    A pipe stat on the top pipe near the stove controlling the stove circulating pump is all,completely independent of the system lex i would have taught.


  • Registered Users, Registered Users 2 Posts: 12 foxy74


    M cebee wrote: »
    shouldn't be much to it

    is the stove heating the water or what's the story

    when i looked at it a while back there was provision for 2 heat sources -unfortunately i can't recall exact details


    The stove will be the hot water and heating. There are 2 heating zones controlled by Room stats and motorised valves. the hot water has its cylinder stat. Its a big stove so its good enough to heat all. i remember coming across something like this before. do i use the aux terminals on systemlex. but not sure how to do it.


  • Registered Users, Registered Users 2 Posts: 12 foxy74


    A pipe stat on the top pipe near the stove controlling the stove circulating pump is all,completely independent of the system lex i would have taught.


    Ya i was thinking that too but will the circulating pump pump through the manifold to heat the house and water?


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    if you take a look at the technical datasheet for systemlex
    http://www.systemlink.ie/images/stories/systemlink/_notes/SystemLex%20-%20Leaflet.pdf

    you'll see the double pole aux relay and 4 inputs

    an input from a stat on your second heat source (stove) can 'lock out' the boiler on one n/c pole

    and activate a MV or zone pump on another n/o pole

    i think the controller for the homezone is the same -it shows the second heat source integrated on page 15
    http://www.systemlink.ie/images/stories/systemlink/Homezone%20Installation%20A5.pdf


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12 foxy74


    M cebee wrote: »
    if you take a look at the technical datasheet for systemlex
    http://www.systemlink.ie/images/stories/systemlink/_notes/SystemLex%20-%20Leaflet.pdf

    you'll see the double pole aux relay and 4 inputs

    an input from a stat on your second heat source (stove) can 'lock out' the boiler on one n/c pole

    and activate a MV or zone pump on another n/o pole

    i think the controller for the homezone is the same -it shows the second heat source integrated on page 15
    http://www.systemlink.ie/images/stories/systemlink/Homezone%20Installation%20A5.pdf


    Thx for that. just to let you know i emailed systemlink about the problem and they sent me this

    SolidFuel&Oil_Mech&Elec.pdf


    Might be of some use to someone here


  • Registered Users, Registered Users 2 Posts: 48 ltz400


    Have installed a systemlex with 2 zones and an oil boiler question is how do i wire the frost stat on the boiler to turn on the rads zone valve

    Any ideas


  • Registered Users, Registered Users 2 Posts: 48 ltz400


    Have installed a systemlex with 2 zones and an oil boiler question is how do i wire the frost stat on the boiler to turn on the rads zone valve

    Any ideas


  • Registered Users, Registered Users 2 Posts: 1,890 ✭✭✭tomdempsey200


    Don't think you do.
    Frost stat adjacent to boiler probably just protects boiler via a auto bypass valve