110v cte sockets

  • 07-06-2011 9:15am
    #1
    Closed Accounts Posts: 4,431 ✭✭✭


    hey

    can anyone confirm rcd isn't required for 110v cte 16amp sockets

    i'm reasonably certain this is the case


Comments

  • Closed Accounts Posts: 82 ✭✭istabraq


    No rcd only a double pole breaker as far as i know


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    yes - i think they're excluded from requirement for rcd

    i'll dig out the rules later


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    ya-it's not required


    it's one of the 'special protective measures'


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Not surprising, as 55v wont be doing much in the way of electric shocks. Even 110v to earth is not very dangerous compared to 230v.
    Just doubling the voltage is a massive step up in the shock recieved in the same circumstances. Just shows how dangerous 400v shocks are.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    supplementary protection against direct contact not exceeding 30ma

    for sockets:

    excepts sockets exceeding 32amp

    selv,pelv,felv,rlv,non-conducting location

    IT equipment and sockets used for isolation


    that's more or less it subject to clauses etc.


    if you do fit rcd/rcbo on 110v it'll be 16amp 10ma rcbo usually

    10ma protection for 110v and 16 or 25amp current rating is the biggest they do for 10ma

    a lot of times they'll use the rcd for 110v or IT equipment anyway


  • Advertisement
  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    robbie7730 wrote: »
    Not surprising, as 55v wont be doing much in the way of electric shocks. Even 110v to earth is not very dangerous compared to 230v.
    Just doubling the voltage is a massive step up in the shock recieved in the same circumstances. Just shows how dangerous 400v shocks are.


    true robbie