Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

How to supply power to garage?

  • 06-05-2011 10:46am
    #1
    Registered Users, Registered Users 2 Posts: 2,340 ✭✭✭


    Hi Folks,

    Our house has an attached garage, but the garage doesn't have any sockets, just a light.
    I want to get a feed into the garage for sockets, but do it as unobtrusively as possible.

    On the pic below, the red rectangle shows the location of the fuse box in the hall. I had an electrician over the other day and he suggested drilling out from the fuse box and tacking some 2.5 along the wall (marked by the red line). I could rake out some mortar between the bricks and sink the cable to help hide it.

    But before I go ahead with it, I'm looking for suggestions for other ways of doing it. I thought a cable could be run through the cavity from the fuse box to inside the garage and hide the run completely, but the electrician said this would be very difficult.

    Any other suggestions?

    Thanks

    wiringv.jpg


Comments

  • Registered Users, Registered Users 2 Posts: 260 ✭✭sparks24


    what size cable is feeding the garage already?

    would be tricky enough to get a new cable in but your meter box is there also close by and you could use that as an access to get the cable that far anyway


  • Registered Users, Registered Users 2 Posts: 3,423 ✭✭✭Avns1s


    How many sockets do you need and what will they be used for?

    If its a small number and a small loading, I would be looking to see if there was a socket on the house side of the wall dividing the garage and house.

    I would then drill through the wall and surface mount the sockets looped together with 2.5 T&E in surface mounted trunking.

    I wouldn't consider the proposal of covering the cable with mortar between the bricks a safe proposition. Nor is it that easy.


  • Registered Users, Registered Users 2 Posts: 5,401 ✭✭✭DublinDilbert


    As others have said you could try get it to the meter box (could follow meter tails) then workout how to get it the remaining 2 feet. As it's a red brick construction I assume there's a cavity inside the wall, this could possibly be used for the last few feet.

    The easier approach might be to find a socket that's back to back with the garage, possibly even an upstairs one and tap off from there.


  • Registered Users, Registered Users 2 Posts: 2,340 ✭✭✭Cmar-Ireland


    Cheers for the replies.

    The supply to the garage is just 1.5 to the light fitting.

    I want to use it for regular garage power tools, grinder, saws, drill etc, but also for a small mig welder. Probably put 4 sockets (2x double metal socket boxes)
    The wall between the garage and house is the kitchen wall and it does have sockets I could drill through from.
    But I would prefer to have the garage on a seperate breaker than to use the ring main or kitchen supply.

    I could stitch drill the mortar around a block in the garage and so open up access to the cavity. Would that allow a cable to be feed directly to the fuse box?


  • Registered Users, Registered Users 2 Posts: 260 ✭✭sparks24


    ya if you get a long bit and drill at an angle out towards the meter box from inside the garage you should get into the cavity no problem and from there with a set of cable rods you can go between the fuse board to the meter box back into the garage with your supply. you might get lucky and get it first time or more likely it will take a couple goes with someone giving you a hand.

    but have a think about if its worth the trouble, how often will you be using a heavy load in the garage? if you are going to be doing a lot of welding i'd say put in a new supply it really sucks up the current and you would want to use a c type MCB because it has a very high inductive load and you don't want it tripping out on you all the time.


  • Advertisement
  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    prob waste of time branching off an existing house circuit for garage

    -if you're planning on welding etc.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Maybe you could remove skirting below fuseboard inside house over as far as garage, bring a new socket circuit down dry lining and out where skirting was, run cable along at floor level, it can easily be pushed in behind bottom of plaster boards right at floor level, and once its over as far as the garage, drill through and bring the cable in. And replace skirting.

    If the skirting does not go over far enough to be over as far as the start of garage, and there is a wall in the way, you just remove the skirting on the other side of wall but still along the side wall of house, go through the wall that was in the way, and same as above, once as far as garage, drill through for cable.

    Would need to see plan of house around the area of the garage to see though.


  • Registered Users, Registered Users 2 Posts: 2,340 ✭✭✭Cmar-Ireland


    I wouldn't be doing a lot of welding, but it would be nice to be able to!
    Was looking at the cable rods and thinking about how I would get a cable from the back of the fuse box down through the cavity. I wouldn't have thought the rods would be able to pull a 2.5 cable through?

    Just looking at the layout inside, directly below the fuse box there is a double socket just above the skirting. Could the cable going to the socket from the fuse box be used to draw another cable down to skirting level and then I could run the cable as robbie suggested?


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Just looking at the layout inside, directly below the fuse box there is a double socket just above the skirting. Could the cable going to the socket from the fuse box be used to draw another cable down to skirting level and then I could run the cable as robbie suggested?

    If the wall the fuseboard is on extends unobstructed over as far as the edge of the garage, then it should be possible if its a dry lined wall the board is on. If it is dry lined its usually easy enough to get a cable down without using existing socket wiring as draw wires. A piece of mini trunking lid is the perfect item for testing the dry lined space and for pulling up cables. I often used existing socket positions as an aid to fish the trunking lid up to the board and down to the floor for a cable run.

    Or you could lift boards upstairs and wire from the board over to where the roof space of the garage is as another option, and into garage that way.

    If your getting a sparks they should see all the options.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    + 1 to what Robbie just said

    However, if it was my house I would drill out through the back of the fuse board and run 6 sq. cables in steel conduit. I would then paint the conduit and grow a climbing type plant over it to hide it!

    This would be quite neat, simple, give future capacity and most importantly be safe giving a high degree of mechanical protection.

    I would consider having a local board in the garage.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,340 ✭✭✭Cmar-Ireland


    planmr.jpg

    Thats where the mcb board is in relation to the meter box and garage.
    I'm now thinking of running the cable internally, using timber strips routed out to hide the cable. The timber would be up against the skirting and run under the stairs. I can then angle drill from under the stairs into the garage.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Looking at that layout, removing the skirting looks even better. And a 6 square like 2011 suggested can be as easily ran that way like the 2.5 could of once it is a dry lining wall. Cable behind skirting. through bottom of stairs and into garage from under the stairs.

    Another possibility is run the cable up the edge of the stairs to the top by cutting out small squares from the plasterboard and fishing the cable right up, and out to the garage. Very easy to then patch the wall along the stairs edge.

    The conduit idea outside would be the easiest, and not the worst either. You would have a round end box on the outside where the fuseboard is and conduit into the side of the garage.

    But i have often done the skirting board removal method. I would not be big into the idea of surface wood with a cable cut into it myself. But maybe it would do especially if just over the skirting.


  • Registered Users, Registered Users 2 Posts: 229 ✭✭ShamFeen


    Good ideas but, you're not allowed run cables behind a skirting anymore. Obviously this can be dangerous if someone decides to put more fixings into the board.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    ShamFeen wrote: »
    Good ideas but, you're not allowed run cables behind a skirting anymore. Obviously this can be dangerous if someone decides to put more fixings into the board.
    If sufficient mechanical protection is provided (such as steel conduit) this is permitted.

    However, I would still go with you suggestion above.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    More fixings anywhere in a house can hit cables. Maybe its time to do houses in steel conduit now to eliminate every possible risk.


  • Registered Users, Registered Users 2 Posts: 2,340 ✭✭✭Cmar-Ireland


    I think the way to go with this is to drop the cable down from the mcb board to floor inside and run it behind the skirting. There is no danger of screwing/nailing into it as it is two feet from the stairs horizontally and from there it will be under the stairs.
    I'd do as much of the run as I can and get an electrician to do the connections. Should I use 2.5 or 6sq ? I don't think it's worth it to fit a mini mcb board in the garage as it already has a light circuit and the new supply will just be for the sockets.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Run 6 square as 2011 suggested, then you can put a small MCB board in the garage, and a 32amp MCB feeding it in the main MCB board in the hall. That will give you far better options in the garage then for any additional circuits in future.


  • Registered Users, Registered Users 2 Posts: 229 ✭✭ShamFeen


    robbie7730 wrote: »
    More fixings anywhere in a house can hit cables. Maybe its time to do houses in steel conduit now to eliminate every possible risk.


    Oh I know that Robbie just passing on the wise mutterings from the Reci Inspector a few days ago. To run a cable horizontally, it must be up two metres off the floor level. But as you stated anyone hammering a nail in for a picture can hit any cable in a wall.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    dunno what rule that is-never heard of it


    there's 2 small sections in the rules on concealed wiring-they're fairly simple


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    M cebee wrote: »
    dunno what rule that is-never heard of it
    Neither did I.

    Surely it conflicts with skirting trunking??


    If it is not obvious where cables are installed suitable mechanical protection will ensure that nails can not cause issues.


  • Advertisement
  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    wires less than 50mm back in solid wall or partition

    -have to go horizontal or vertical to a switch/socket etc

    -or be ran less than 150mm from ceiling or corner


    -otherwise use SWA or steel


    haven't the rules in front of me but i think
    that's the jist of it


  • Registered Users, Registered Users 2 Posts: 2,401 ✭✭✭evosteo


    you're not allowed run cables behind a skirting anymore

    what a load of bs, some of them inspectors have nothing better to do than make up their own rules, their never happy:confused::confused::confused:


Advertisement