Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

GLOWWORM 24ci--Helppp!!!!

  • 19-02-2011 1:14pm
    #1
    Registered Users, Registered Users 2 Posts: 5


    Bolier problem since christmas.Tought initially it was water pressure reduction due to cold weather.Pressure drops below .7 bar and pilot light failed to come on.Tradesman put in vent loop to bring up Bar pressure when it dropped.This worked for a while but now has finally packed up.

    Have had a Glowworm expert out who fluted around with it and has since been uncontactable.Last night bar 1.4 and suddenly dropped again.Today pressure dropped to .5 and boiler has died altogether.

    Anybody know how to help or anybody tthey could recommend.

    Dun Laoghire area.

    JIM


Comments

  • Registered Users, Registered Users 2 Posts: 1,492 ✭✭✭roy rodgers


    I dont think its any thing to do with the boiler, the boiler is only doing what it should be doing when the pressure is low.
    There should be a filling loopin the hot press which needs to be turned on for about 15 seconds or until the pressure has reached over 1 bar at least.
    Try that first and see how the boiler works, if the pressure keeps raising while the boiler is running to over 3 bar well it could be an expansion problem but we'll watch this space till we see how the boiler goes.


  • Registered Users, Registered Users 2 Posts: 5 jim1960


    Hi Roy

    Thanks for advice.Boilerman finally arrived .Had been trying what you were suggesting before and even that was not working.Boiler man installed expansion Tank and Boiler has been working perfect since.Hopefully,this will cure it.

    Thanks

    Jim


Advertisement