Central Heating Low Pressure

  • 19-01-2011 6:00pm
    #1
    Registered Users, Registered Users 2 Posts: 111 ✭✭


    Just wondering if anyone elses heating is displaying fault codes relating to low pressure, I gets it going after running the hot water tap for ages and a couple resets, the thing I ask is I noticed 2 other people with the same prob although different parts of the city. Should I ring the corporation or will this sort itself out?


Comments

  • Registered Users, Registered Users 2 Posts: 251 ✭✭Deisekickboxing


    Boiler
    May need a service


  • Registered Users, Registered Users 2 Posts: 497 ✭✭The blue blaa


    Did you try topping up the pressure??? should be a fill valve where your boiler is or else one in the hot press top it up between 1.5 - 2 bar pressure there will be a gauge on ur boiler indicating the pressure.. Corporation have nothing to do with it..


  • Banned (with Prison Access) Posts: 483 ✭✭tom thum


    Did you try topping up the pressure??? should be a fill valve where your boiler is or else one in the hot press top it up between 1.5 - 2 bar pressure there will be a gauge on ur boiler indicating the pressure.. Corporation have nothing to do with it..
    i thought it was supposed to be at 1 bar cold , in order for it to work ok.?


  • Registered Users, Registered Users 2 Posts: 497 ✭✭The blue blaa


    1 bar pressure cold as you call it,would be 1.5 when boiler in use.. because of expansion vessel inside boiler,but your right it would better off on 1 bar cold.. my mistake tom thum