cs-250 aritech

  • 12-12-2010 10:12pm
    #1
    Registered Users, Registered Users 2 Posts: 75 ✭✭


    Can anyone tell me whats wrong. Internal bell wont work(replaced still no noise) External bell clicking like mad.I will get a new (12v 7.2ah) battery back up tomorrow fault coming up battery VT battery Ld persume main battery five/six years old.Would this fix all problem's?

    i have checked mains 230v OK
    transformer seems Ok
    13vdc at bottom of panel(connect red and black for output side 13.0dc)
    BUT when i put on battery back up it drops to 6vdc Battery causing problem.would it be ok to leave battery off till get new one.

    External bell stopped clicking since took of battery.

    Thanks:confused:


Comments

  • Registered Users, Registered Users 2 Posts: 11,855 ✭✭✭✭altor


    The battery VT fault or battery Ld fault refers to you needing to check the connections on the battery, if it is connected you will need a new battery. The panel does not have fuses so if there is a problem with a cable it will click in like you say. I would also check the connections to both internal and external bell in case there is a problem with the cable.


  • Registered Users, Registered Users 2 Posts: 75 ✭✭bombers


    thanks
    i will have a look again tomorrow when i get new battery:)


  • Registered Users, Registered Users 2 Posts: 11,855 ✭✭✭✭altor


    Your welcome, as there are no fuses in the panel I would check for cables touching in the panel terminals. That might be the cause of the clicking as it takes a few minutes for it to reset. If it is still happening you will need to check both ends of the cable with a multimeter.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    If you have no meter disconnect both bells and try connecting them directly into the panel on a short lenght of cable one by one.
    This will confirm or eliminate a cable problem.


  • Registered Users, Registered Users 2 Posts: 75 ✭✭bombers


    :mad:everything going good since replaced battery except int bell.i have checked for voltage and it is getting 13vdc when do test .will get another one tomorrow hopefully will sort it out .any ideas incase still doesnt work.i have + & - in 3 & 4 terminals of bell ,does this sound right?

    Thanks Again


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 11,855 ✭✭✭✭altor


    bombers wrote: »
    :mad:everything going good since replaced battery except int bell.i have checked for voltage and it is getting 13vdc when do test .will get another one tomorrow hopefully will sort it out .any ideas incase still doesnt work.i have + & - in 3 & 4 terminals of bell ,does this sound right?

    Thanks Again

    That is incorrect.

    If you look at the board you will see a small bell, this is for the internal bell. It is terminal 6 + 7 -

    You have 12v 1+2, data 3, keypad 4+5, internal bell 6+7, external bell 8+9.

    Hope this helps.


  • Registered Users, Registered Users 2 Posts: 75 ✭✭bombers


    :):)Back in action again

    thanks for all the help

    p.s. 3 & 4 in the int bell not in main panel


  • Registered Users, Registered Users 2 Posts: 11,855 ✭✭✭✭altor