plumbing and heating

  • 28-11-2010 8:29pm
    #1
    Closed Accounts Posts: 9


    hi guys
    have a problem with an oil burner,
    the boiler rus ok but when it reaches temputure,
    it knocks itself off and you have to reset the red button,
    i think it might be the control box but im not sure,
    would appreciate any help thanks


Comments

  • Registered Users, Registered Users 2 Posts: 4,826 ✭✭✭meercat


    which red button
    if its on the top,try turning the thermostat beside it down a fraction
    if it is this high limit stat,fit a pipestat to the pump and this will help


  • Closed Accounts Posts: 9 roc1980


    hi meercat
    its not the high limit stat its the one on
    the burner and the boiler will run
    once you reset it, and will keep goin
    into lockout once tempature is reached
    has me puzzled


  • Registered Users, Registered Users 2 Posts: 473 ✭✭nophd08


    roc1980 wrote: »
    hi meercat
    its not the high limit stat its the one on
    the burner and the boiler will run
    once you reset it, and will keep goin
    into lockout once tempature is reached
    has me puzzled

    Is your rads and water heating, If not then its prob your circulating pump, If they are heating as normal, it might be thermostat thats goosed.
    Try turning stat down while burner is running and see if it switches off. If it switches off and goes to lockout then it might be control box or stat problem.


  • Registered Users, Registered Users 2 Posts: 251 ✭✭GopErthike


    It's a problem with the burner, temperature won't bring on that light.
    Possibly the oil pump seizing when it gets hot or as was mentioned a control box problem.


  • Closed Accounts Posts: 11 Newnews


    Sorry to hijack the thread, but I think I am suffering from the same problem. It's been happening for over a year, and the cold snap has inspired me to look into it. What happens in my case is the following: turn on the heating, burner will start up and heat the radiators and water. When it hits the high limit stat it locks out, and will only restart when I press the reset button the burner. Over the weekend I cleaned out the combustion chamber, the photocell and replaced the thermostat, but it's still not restarting when the temperature drops - any ideas. The radiators to get hot, (but not 'piping hot' ) so I don't think it's the circulation pump. Anyone have an ideas? Only other thing is there is no stat in the house, just a timer and on/off switch.

    Thanks,

    newnews


  • Advertisement
  • Closed Accounts Posts: 905 ✭✭✭FUNKY LOVER


    Newnews wrote: »
    Sorry to hijack the thread, but I think I am suffering from the same problem. It's been happening for over a year, and the cold snap has inspired me to look into it. What happens in my case is the following: turn on the heating, burner will start up and heat the radiators and water. When it hits the high limit stat it locks out, and will only restart when I press the reset button the burner. Over the weekend I cleaned out the combustion chamber, the photocell and replaced the thermostat, but it's still not restarting when the temperature drops - any ideas. The radiators to get hot, (but not 'piping hot' ) so I don't think it's the circulation pump. Anyone have an ideas? Only other thing is there is no stat in the house, just a timer and on/off switch.

    Thanks,

    newnews

    if the thermostat is ok the high limit stat should not kick in unless you have it set too high.

    no offence but you should really get in an engineer,for the sake of a few quid it will save you headaches and damaging it more.


  • Registered Users, Registered Users 2 Posts: 1,118 ✭✭✭Sparkpea


    Newnews wrote: »
    Sorry to hijack the thread, but I think I am suffering from the same problem. It's been happening for over a year, and the cold snap has inspired me to look into it. What happens in my case is the following: turn on the heating, burner will start up and heat the radiators and water. When it hits the high limit stat it locks out, and will only restart when I press the reset button the burner. Over the weekend I cleaned out the combustion chamber, the photocell and replaced the thermostat, but it's still not restarting when the temperature drops - any ideas. The radiators to get hot, (but not 'piping hot' ) so I don't think it's the circulation pump. Anyone have an ideas? Only other thing is there is no stat in the house, just a timer and on/off switch.

    Thanks,

    newnews

    probably a new thermostat needed


  • Closed Accounts Posts: 11 Newnews


    Thanks Funky lover/spark pea - but the thermostat was replaced on Saturday with no change in the burner lockout problem. I was hoping to have an idea what was wrong before engaging an engineer to avoid being fleeced.


  • Closed Accounts Posts: 905 ✭✭✭FUNKY LOVER


    Newnews wrote: »
    Thanks Funky lover/spark pea - but the thermostat was replaced on Saturday with no change in the burner lockout problem. I was hoping to have an idea what was wrong before engaging an engineer to avoid being fleeced.


    is the high limit stat kicking in and then burner locking out?

    your thermostat should be knocking off the burner before high limit stat takes over.


  • Closed Accounts Posts: 11 Newnews


    It seems to be a bit of both - if I set my thermostat low, the burner will knock off, but if I then raise the thermostat the burner will instantly fire up. However, if I don't touch the thermostat, the burner will not kick in, instead it will go in to lock out. If I set the thermostat low, the burner will fire up, heat to the required temp and turn off. If I let the system cool, the burner will not fire up on it's own, but if I turn off and on the power it will usually (but not always) fire up.

    However, if I set the thermostat to it's max, the burner will knock off (before the radiators get too hot) and will go in to lock out. So I'm a bit confused.

    All the radiators have been bled and every radiator gets to a very similar temperature. All thoughts are welcome!


  • Advertisement
  • Closed Accounts Posts: 9 roc1980


    cheers lads for the info in the end it was a
    dodgy fuel pump changed the burner as it was really
    old anyways.didnt realise they now come as kero or diesel
    oil,not like the old ones were you can adjust the
    pressure, thanks again lads