Help with central heating

  • 09-11-2010 1:01pm
    #1
    Registered Users, Registered Users 2 Posts: 316 ✭✭


    Having some problems with the heating in the house, none of the downstairs heaters are working and only 2 in the upstairs are working. The heating system is oil and is run from a stanley oil cooker.

    Im useless at heating systems so if anyone has any ideas?

    and also I opened this valve, might be a drain valve and now it is dripping, how do I stop it?

    The black nozzle and the pipe going straight down just opens at the end

    5161257632Photo0285.jpg
    a%3E


Comments

  • Registered Users, Registered Users 2 Posts: 1,118 ✭✭✭Sparkpea


    that looks like a safety valve to me, if you've opened it and its leaking then it needs replaced. in the short term u could put a pushfit stop end on it to stop it leaking but this isn't recommended for more than a few days as a safety valve is there as a safety device.


  • Registered Users, Registered Users 2 Posts: 2,676 ✭✭✭kay 9


    Did ya vent the rads? As sparkpea has said don't block that safety valve for long or at all if possible. Get it replaced. MAybe try flicking it a couple of times and it will seal itself.


  • Closed Accounts Posts: 302 ✭✭ntpm


    Sounds like a pump issue.

    I suspect that your hot water cylinder is still getting hot from the stove via gravity. The couple of rads upstairs are probably working on gravity as well...
    There should be a pipe stat that switches on a circulation pump to push water round the rads.

    Check the stat and the that the pump is spinning ( carefully open large screw on front of pump, Water shpuld come out and if you place a screw driver in side you should feel the pump turning,,,, it may be air locked or jammed.

    As stated earlier do not block the Pressure relief valve outlet.
    As a quick fix (semi perminent) you can buy anther PRV and a couple of fittings and connect it in line (series) with the other on. This saves draining the system.