  • 15-10-2010 3:11pm
    #1
    Registered Users, Registered Users 2 Posts: 91 ✭✭


    Hi i am just wondering how much more expensive is it to go with an Air to Water heat pump and underfloor heating compaired to an oil condensing boiler rads and a stove with back boiler and solar panels . Would they be much of a difference between the two, Also if anyone has an air to water heat pump how do they find the bills ect . I have heard alot of horror stories has anyone hear experienced these.


Comments

  • Registered Users, Registered Users 2 Posts: 12,822 ✭✭✭✭galwaytt


    What type of construction are you using ?

    The reason I ask is that we built a pair of semi's with NIBE air-water units, and they work well, with a mix of rads/ufh............but in a very high spec, highly airtight house.

    If you're not doing that, then I'd be afraid that it would run too long, too often, and ESB bills would be what you'd expect...........it's a low-grade heat appliance, so I'm not sure how it would cope with a big big heat demand on an on-going basis.

    They're also not cheap to buy.

    Ode To The Motorist

    “And my existence, while grotesque and incomprehensible to you, generates funds to the exchequer. You don't want to acknowledge that as truth because, deep down in places you don't talk about at the Green Party, you want me on that road, you need me on that road. We use words like freedom, enjoyment, sport and community. We use these words as the backbone of a life spent instilling those values in our families and loved ones. You use them as a punch line. I have neither the time nor the inclination to explain myself to a man who rises and sleeps under the tax revenue and the very freedom to spend it that I provide, and then questions the manner in which I provide it. I would rather you just said "thank you" and went on your way. Otherwise I suggest you pick up a bus pass and get the ********* ********* off the road” 



  • Registered Users, Registered Users 2 Posts: 1 flash333


    thinking about about air to water heat pump with underfloor heating on ground floor,radiators on first floor. has anyone installed this in the last 12 months, how hot do the radiators get,what about the esb bills,esp for the winter have you a back up system?


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    is this a new build or renovation
    are you building to Part L 2011 ?


  • Registered Users, Registered Users 2 Posts: 25 citywide


    flash333 wrote: »
    thinking about about air to water heat pump with underfloor heating on ground floor,radiators on first floor. has anyone installed this in the last 12 months, how hot do the radiators get,what about the esb bills,esp for the winter have you a back up system?


    Hi did you get any advice or information on air to water heat pump I am thinking of using the same but under floor heating up & down. Stairs


  • Registered Users, Registered Users 2 Posts: 228 ✭✭blast06


    Moved into my new house Aug 31st. ..... its part L 2011 compliant, BER A2.

    Have a Danfoss air to water heat pump with underfloor downstairs (downstairs being 75% of total living area) and rads upstairs. Also have a BEAM MHRV.

    I find the comfort of living absolutely fantastic. I have not turned on the rads for the 2 upstairs bedrooms yet (have double height front hall) and temp upstairs has never once deviated from 20 or 21 degrees.

    Total price of underfloor, plus 3 rads upstairs plus heat pump including hot water tank etc was 16K.
    If you're house is part L compliant then i think you'd be bonkers to go with oil burner, rads, stove back burner and solar panles.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    blast06 wrote: »
    Moved into my new house Aug 31st. ..... its part L 2011 compliant, BER A2.

    Have a Danfoss air to water heat pump with underfloor downstairs (downstairs being 75% of total living area) and rads upstairs. Also have a BEAM MHRV.

    I find the comfort of living absolutely fantastic. I have not turned on the rads for the 2 upstairs bedrooms yet (have double height front hall) and temp upstairs has never once deviated from 20 or 21 degrees.

    Total price of underfloor, plus 3 rads upstairs plus heat pump including hot water tank etc was 16K.
    If you're house is part L compliant then i think you'd be bonkers to go with oil burner, rads, stove back burner and solar panles.

    really intersted in your performance numbers - I used more heating than I should have done last year (around 1500Kwh)
    a) the problem described here - https://www.facebook.com/Passive.House.Wexford/posts/174801372724975?comment_id=251690&offset=0&total_comments=1&notif_t=feed_comment
    b) because I set the heat curve to 28 degrees but this is still too much - take the last couple of days - floor is at 21.5 deg - but the heat curve detected the cold weather overnight and run the HP for about 2hrs. The sun the next day was warm and heated the house up - so the HP efforts were wated

    I need to do some more clever monitoring to resolve this issue


  • Registered Users, Registered Users 2 Posts: 228 ✭✭blast06


    Yes - i know the problem ! .... albeit that it was only really in the warm spell in September i had this problem. For past couple of weeks, everything has been great. I think part of this is due to it only being now that MRHV is offering full value ...... i only connected a drainage pipe to it 2-3 weeks ago so i think humidity levels in the house were a small big higher than they might otherwise have been until i done this.
    It is only my upstairs that has the very consistent temperature. I still have not turned on heating up there and it was 19 degrees this morning (0 degrees outside at 7am) - perfect for bedrooms.

    I have only started loking at my stats closely since i saw your reply. I have been too busy with work and a million and 1 other things since i moved in to worry about this. I am also waiting on an app from Danfoss supplier to monitor this on the fly.
    My stats for last few days as per below. I will (obviously!) use a lot more kWh than you for heating (my assumption is that 50% of heating will be daytime and 50% nighttime) but i still think the bill here is for next to nothing for keeping a 2600 sq ft house at contant 20-21 degrees 24/7 (although maybe i should hold my smoke on that statement until after a really cold spell !)

    Compressor Heating Hot Water Heating Units kWh Hot Water Units kWh Heating cost Hot Water cost Total Cost
    2013-10-30 217 152 63
    2013-10-31 223 157 63 11.25 0 1.42 0.00 1.42
    2013-11-01 228 162 64 11.25 3.15 1.42 0.53 1.95
    2013-11-02 234 167 65 11.25 3.15 1.42 0.53 1.95
    2013-11-03 241 173 65 13.5 0 1.70 0.00 1.70


    PS ... i set my heat curve to 29 from the day i moved in and haven't changed that yet


  • Registered Users, Registered Users 2 Posts: 1,504 ✭✭✭BarneyMc


    blast06 wrote: »
    I have not turned on the rads for the 2 upstairs bedrooms yet (have double height front hall) and temp upstairs has never once deviated from 20 or 21 degrees.

    Would this suggest that for a very low energy house UFH upstairs is unnecessary and low energy rads are the way to go? Is there much price difference?


  • Registered Users, Registered Users 2 Posts: 1,504 ✭✭✭BarneyMc


    blast06 wrote: »
    Yes - i know the problem ! .... albeit that it was only really in the warm spell in September i had this problem. For past couple of weeks, everything has been great. I think part of this is due to it only being now that MRHV is offering full value ...... i only connected a drainage pipe to it 2-3 weeks ago so i think humidity levels in the house were a small big higher than they might otherwise have been until i done this.
    It is only my upstairs that has the very consistent temperature. I still have not turned on heating up there and it was 19 degrees this morning (0 degrees outside at 7am) - perfect for bedrooms.

    I have only started loking at my stats closely since i saw your reply. I have been too busy with work and a million and 1 other things since i moved in to worry about this. I am also waiting on an app from Danfoss supplier to monitor this on the fly.
    My stats for last few days as per below. I will (obviously!) use a lot more kWh than you for heating (my assumption is that 50% of heating will be daytime and 50% nighttime) but i still think the bill here is for next to nothing for keeping a 2600 sq ft house at contant 20-21 degrees 24/7 (although maybe i should hold my smoke on that statement until after a really cold spell !)

    Compressor Heating Hot Water Heating Units kWh Hot Water Units kWh Heating cost Hot Water cost Total Cost
    2013-10-30 217 152 63
    2013-10-31 223 157 63 11.25 0 1.42 0.00 1.42
    2013-11-01 228 162 64 11.25 3.15 1.42 0.53 1.95
    2013-11-02 234 167 65 11.25 3.15 1.42 0.53 1.95
    2013-11-03 241 173 65 13.5 0 1.70 0.00 1.70


    PS ... i set my heat curve to 29 from the day i moved in and haven't changed that yet

    Very impressive figures! How come you hot water costs are zero some days?


  • Registered Users, Registered Users 2 Posts: 228 ✭✭blast06


    I couldn't say re low energy rads.
    First of all i wouldn't say i have a very low energy house - it is just about A2.
    I have normal rads in the 2 bedrooms upstairs and bathroom upstairs with 1 mid-sized skylight per room. Walls and sloped ceilings have 100mm rafterloc, then air-tightness membrane then 62.5mm insulated slab. On flat ceiling part it is normal slab, air-tightness membrane, 100mm rafterloc plus 200mm wool.
    I priced the cost of the low energy rads but i didn't think the cost-benefit figures could justify it and so far i am right .... the payback would be a ridiculous number of years.
    However, by the end of next March, i would be in a better position to fully comment.

    Re the hot water figures ..... OK, the zero figures aren't strictly correct ! Take the figures for the 31st Oct - the number of hours the compressor had been running in total for hot water was 63 by end of that day. By end of the following day it hadn't ticked over to the 64th hour .... so it was probably a case of 63 hours and a few minutes by end of 31st and by end of Nov 1st it was probably just a few minutes shy of 64 hours in total (or else we're a smelly family and didn't wash that day :) ). It will balance out over a week or more.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    blast06 wrote: »
    - it is just about A2.
    ok ;)

    Re the hot water figures ..... OK, the zero figures aren't strictly correct ! Take the figures for the 31st Oct - the number of hours the compressor had been running in total for hot water was 63 by end of that day. By end of the following day it hadn't ticked over to the 64th hour .... so it was probably a case of 63 hours and a few minutes by end of 31st and by end of Nov 1st it was probably just a few minutes shy of 64 hours in total (or else we're a smelly family and didn't wash that day :) ). It will balance out over a week or more.

    Yes this happens

    Can I suggest a couple of things
    1 - set the heating at a set back temp of say 18 from 06am -> 23pm - and see how you get on this will force you onto night rate and save a bit

    you can look at the supply/return temps to see how things went - I turned of a week ago and have lost just 0.5 degrees but will run it tonight to top it up again - love to do this programmatically one day

    2 - same with the h/w - turn it off (of course depending on usage) from say 4pm->11pm - this again will cause the top up to happen on cheap elec


    question: how did you get the Kw vs hrs - what factor did you multiply by for each of the hrs


  • Registered Users, Registered Users 2 Posts: 1,504 ✭✭✭BarneyMc


    So you both use the night rate electric meter?


  • Registered Users, Registered Users 2 Posts: 228 ✭✭blast06


    Thanks FC. I need to check this..... i didn't know i could do it. I presume of course you do not mean to manually turn it on/off at those times.....

    Re Kw versus hours ..... just multiply the number of hours compressor was running by the kWh rate, i.e.: 2.5 for the heating and 3.5 for the hot water. Note, since i posted, i know i got my usage rates wrong, i.e.: i was assuming 2.25 for heating and 3.15 for hot water but was corrected when i was on the phone to the supplier today.

    Barney - yes, night rate for sure


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    blast06 wrote: »
    Thanks FC. I need to check this..... i didn't know i could do it. I presume of course you do not mean to manually turn it on/off at those times.....
    not use the calendar function on the unit (assuming its an AQ)

    Re Kw versus hours ..... just multiply the number of hours compressor was running by the kWh rate, i.e.: 2.5 for the heating and 3.5 for the hot water. Note, since i posted, i know i got my usage rates wrong, i.e.: i was assuming 2.25 for heating and 3.15 for hot water but was corrected when i was on the phone to the supplier today.

    Barney - yes, night rate for sure

    where did you get those numbers from ?


  • Registered Users, Registered Users 2 Posts: 1,504 ✭✭✭BarneyMc


    Just did a bit of digging and it seems like these are the current figures when using a night meter:

    Normal 24 Hour Meter
    Annual Standing Charge of €165
    Unit Price of 15.3 cent per unit

    Night Saver Meter
    Annual Standing Charge of €218
    Unit Price of 16.3 cent per unit from 8AM to 11PM
    Unit Price of 8.1 cent per unit from 11PM to 8AM

    Yip, makes sense to me to use a Night Saver meter if going down the heat pump route. Seems like this would favour a slab rather than screed floor finish for the UFH so the HP could use cheap units at night? Would a ground source HP be better when used with a ground source HP also?


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    BarneyMc wrote: »
    Would a ground source HP be better when used with a ground source HP also?
    ??


  • Registered Users, Registered Users 2 Posts: 228 ✭✭blast06


    fclauson wrote: »
    where did you get those numbers from ?

    From the supplier .... he detailed these rates in the original quote and more or less clarified today when i gave him a call on a few points.
    Given that you are asking though i am now asking myself again ..... so i had a look here (the 11 KwH one).... http://heating.danfoss.com/PCMPDF/dhp-aq_VDGFE402.pdf
    The 3.5 figure i guess comes from the compressor (3.3) and fan (0.2) but now i am now sure where he is getting the 2.5 for for heating. I need to get in touch with him again.

    PS .... thanks re the tips. I figured out the 'blocking' for hot water. Presuming this could say result in 50% of hot water heating happening between 11pm and 7am instead of 100% during daylight hours then i estimate this will save me ~€50-60 per annum. Cheers !
    I'm a bit nervous about playing with the heating just yet though cos herself is beginning to come round to the idea that it was worthwhile pumping so much of the budget into securing an A2 house with this heating system, HRV, etc with not enough money left for all the furnitute she wanted (she only realised this when i had already committed to securing an A2!!) ..... so i don't want to find the house "not warm enough" by playing with the settings just yet !!


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    blast06 wrote: »
    From the supplier .... he detailed these rates in the original quote and more or less clarified today when i gave him a call on a few points.
    Given that you are asking though i am now asking myself again ..... so i had a look here (the 11 KwH one).... http://heating.danfoss.com/PCMPDF/dhp-aq_VDGFE402.pdf
    The 3.5 figure i guess comes from the compressor (3.3) and fan (0.2) but now i am now sure where he is getting the 2.5 for for heating. I need to get in touch with him again.
    you will also find this info in your installation manual for the DHQA
    PS .... thanks re the tips. I figured out the 'blocking' for hot water. Presuming this could say result in 50% of hot water heating happening between 11pm and 7am instead of 100% during daylight hours then i estimate this will save me ~€50-60 per annum. Cheers !
    Your round next time we meet then :P
    I'm a bit nervous about playing with the heating just yet though cos herself is beginning to come round to the idea that it was worthwhile pumping so much of the budget into securing an A2 house with this heating system, HRV, etc with not enough money left for all the furnitute she wanted (she only realised this when i had already committed to securing an A2!!) ..... so i don't want to find the house "not warm enough" by playing with the settings just yet !!
    Chicken -- but do let the house settle down before you tweek - remember you do have (assuming you have a screed/concrete floor) @ 2600 sqm ft - something like 25 tones of thermal mass let alone the walls to hold you heat - you can do the maths to see just how much that is

    one last thing - its published by Danfoss - but some useful info in the attached


  • Registered Users, Registered Users 2 Posts: 1,504 ✭✭✭BarneyMc


    BarneyMc wrote: »
    Would a ground source HP be better when used with a ground source HP also?

    Sorry, not sure what was going on there! :o

    What I wanted to say was, when a HP is working away it's producing hot water for the UFH system. However does that mean the hot water has to be circulated around the UFH system at the same time. In other words is it possible to have your HP run on the night saver rate but have the water circulated later in the day?


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    BarneyMc wrote: »
    Sorry, not sure what was going on there! :o

    What I wanted to say was, when a HP is working away it's producing hot water for the UFH system. However does that mean the hot water has to be circulated around the UFH system at the same time. In other words is it possible to have your HP run on the night saver rate but have the water circulated later in the day?

    Barney - HP works like an old boiler
    for h/w production the heating circ goes HP->tank->HP
    for UFH production it goes HP->UFH->HP

    You screed - depending on size is around 1.8 Tones per M3 - you use this as the thermal store - warm it a little and these it slowly ooses heat - in reality in a well insulated house the screed temp might move 20.5 -to 22 and back again - hence why Zones, or heating coming on in the morning no longer makes sense

    So to answer you question - yes - heat the floor 11pm->6am - and then hope you can coast for the rests of the day - which is what I am doing except I have it back on at 10am to make use of the PV - but I am now questioning this judgement and might not do so


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 228 ✭✭blast06


    Jes, those figures look impresive FC - even if they are published by Danfoss themselves.
    With all this talk of 25 tonnes of thermal mass (i have 18m3 of screed so probably closer to 30 tonnes) i'm getting more tempted to start playing with the heating settings !!
    One question on your reply below: "except I have it back on at 10am to make use of the PV" .... what is PV ?

    Cheers,
    Beers on me!


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    blast06 wrote: »
    Jes, those figures look impresive FC - even if they are published by Danfoss themselves.
    With all this talk of 25 tonnes of thermal mass (i have 18m3 of screed so probably closer to 30 tonnes) i'm getting more tempted to start playing with the heating settings !!
    One question on your reply below: "except I have it back on at 10am to make use of the PV" .... what is PV ?

    Cheers,
    Beers on me!

    PV - photo voltaic-


  • Registered Users, Registered Users 2 Posts: 1,504 ✭✭✭BarneyMc


    fclauson wrote: »

    So to answer you question - yes - heat the floor 11pm->6am - and then hope you can coast for the rests of the day

    I'm not sure of the dynamics of heat release from UFH in screed v concrete but having a slower release concrete floor might work better using the above approach?


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    BarneyMc wrote: »
    I'm not sure of the dynamics of heat release from UFH in screed v concrete but having a slower release concrete floor might work better using the above approach?

    its all physics - density and thermal capacity -do the maths :pac:


  • Registered Users, Registered Users 2 Posts: 228 ✭✭blast06


    OK, i've made the switch .... heating and hot water now only running between 11pm and 7am. If i can get away with this on an ongoing basis then my running costs would be almost ridiculously small ..... below would be the figures for the last 7 days if all electricity was from 11pm to 7am



    Date Heating Units kWh Hot Water Units kWh Heating cost Hot Water cost Total Cost
    2013-10-31 13.25 0 1.11 0.00 1.05
    2013-11-01 13.25 3.5 1.11 0.29 1.34
    2013-11-02 13.25 3.5 1.11 0.29 1.34
    2013-11-03 15.9 0 1.34 0.00 1.26
    2013-11-04 15.9 7 1.34 0.59 1.85
    2013-11-05 15.9 0 1.34 0.00 1.26
    2013-11-06 5.3 7 0.45 0.59 1.01



  • Registered Users, Registered Users 2 Posts: 228 ✭✭blast06


    Barney .... i replied to your DM but i have had problems in the past with DM's so if you don't get the DM reply then send me your mail ID and i can mail you.


  • Registered Users, Registered Users 2 Posts: 120 ✭✭dfader


    blast06 wrote: »
    OK, i've made the switch .... heating and hot water now only running between 11pm and 7am. If i can get away with this on an ongoing basis then my running costs would be almost ridiculously small ..... below would be the figures for the last 7 days if all electricity was from 11pm to 7am



    Date Heating Units kWh Hot Water Units kWh Heating cost Hot Water cost Total Cost
    2013-10-31 13.25 0 1.11 0.00 1.05
    2013-11-01 13.25 3.5 1.11 0.29 1.34
    2013-11-02 13.25 3.5 1.11 0.29 1.34
    2013-11-03 15.9 0 1.34 0.00 1.26
    2013-11-04 15.9 7 1.34 0.59 1.85
    2013-11-05 15.9 0 1.34 0.00 1.26
    2013-11-06 5.3 7 0.45 0.59 1.01


    Blast,
    Thanks for this info - its very useful to those planning similar builds. I know you said your house is A2 and so this question might be somewhat academic and I don't wish to derail the tread, but since ye brought up the topic of thermal mass in the floor, I am curious as to what is your external wall build up exactly?


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    blast06 wrote: »
    Barney .... i replied to your DM but i have had problems in the past with DM's so if you don't get the DM reply then send me your mail ID and i can mail you.

    clear you "sent box " is the trick


  • Registered Users, Registered Users 2 Posts: 1,504 ✭✭✭BarneyMc


    blast06 wrote: »
    Barney .... i replied to your DM but i have had problems in the past with DM's so if you don't get the DM reply then send me your mail ID and i can mail you.

    Message received ;)


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,675 ✭✭✭exaisle


    blast06 wrote: »
    OK, i've made the switch .... heating and hot water now only running between 11pm and 7am.

    Did you do this via a timer on the HP circuit or is there a setting in the HP itself? I have a night rate meter but I haven't tweaked the HP system at all....yet!


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    exaisle wrote: »
    Did you do this via a timer on the HP circuit or is there a setting in the HP itself? I have a night rate meter but I haven't tweaked the HP system at all....yet!


    On the Danfoss unit its all on within the HP controls


  • Registered Users, Registered Users 2 Posts: 2,675 ✭✭✭exaisle


    Thanks....on my (Thermia Atria) unit, there's a section called "EVU and Tariff Control" in the installation manual. The timer is optional but hardly likely to break the bank.....


  • Registered Users, Registered Users 2 Posts: 228 ✭✭blast06


    dfader wrote: »
    Blast,
    Thanks for this info - its very useful to those planning similar builds. I know you said your house is A2 and so this question might be somewhat academic and I don't wish to derail the tread, but since ye brought up the topic of thermal mass in the floor, I am curious as to what is your external wall build up exactly?

    No problem.
    Bear in mind now that i am just of an A2 by the skin of my teeth. Big difference between that and being just shy of an A1 (albeit i think the KwH usage per square metre figure in the BER report i have is miles miles higher than what i will actually use based on current usage rates).

    Anyway, walls are fairly straightforward ..... normal block on outside, 150mm pumped cavity and Quinn lite blocks on inside. I also included the Quinn lites on the first row of internal walls to reduce thermal bridging. I thought after the walls were built that i should have gone for a 200mm cavity but now i'm not so sure based on comfort levels to date and given the extra challenge (and thus cost) of closing the cavity under windows for a 200mm gap plus i guess dearer wall ties. Note also, if you go with Quinn lite, you'd need to be very particular on who you get to plaster it. If you have a contractor then ensure you get feedback/examples on where the plasterer has plastered Quinn lites before.


  • Registered Users, Registered Users 2 Posts: 120 ✭✭dfader


    blast06 wrote: »
    OK, i've made the switch .... heating and hot water now only running between 11pm and 7am. If i can get away with this on an ongoing basis then my running costs would be almost ridiculously small ..... below would be the figures for the last 7 days if all electricity was from 11pm to 7am



    Date Heating Units kWh Hot Water Units kWh Heating cost Hot Water cost Total Cost
    2013-10-31 13.25 0 1.11 0.00 1.05
    2013-11-01 13.25 3.5 1.11 0.29 1.34
    2013-11-02 13.25 3.5 1.11 0.29 1.34
    2013-11-03 15.9 0 1.34 0.00 1.26
    2013-11-04 15.9 7 1.34 0.59 1.85
    2013-11-05 15.9 0 1.34 0.00 1.26
    2013-11-06 5.3 7 0.45 0.59 1.01


    Blast,
    Thanks again. Would be good to hear back from you again with this info after a cold snap. ie. sub zero external air temperatures.


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    dfader wrote: »
    Blast,
    Thanks again. Would be good to hear back from you again with this info after a cold snap. ie. sub zero external air temperatures.


    I'll also try to provide numbers - but interested in your findings


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 84 ✭✭Mixupat


    Is airtightness and MHRV key to the success of running a heat pump? Will it perform much worse without airtightness and electric bills shot up.


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    Any heating systems performance is based on insulation and air tightness regardless of heating type


  • Registered Users, Registered Users 2 Posts: 228 ✭✭blast06


    My latest figures as below.
    A few comments ....
    • i didn't persist with leaving the heating on during night time hours only. Wasn't brave enough - i just left it running during night hours on nov 6th
    • I was messing with the heat curve on both the 9th and 22nd where i increased it from 29 to 33 for a 24 hour period just to see the impact. The one on the 22nd also coincided with the coldest of the cold spell.... probably added about 50c to €1 on 22nd
    • And to recap ..... it is a 2600 sq ft house (9' ceilings) that just about scraped an A2 with a Danfoss AQ-11Kw air to water heat pump.... located in the midlands at a highish (for midlands) 115m ASL elevation


    Heating Reading Hot Water Reading Heating Units kWh Hot Water Units kWh Heating cost Hot Water cost Total Cost
    2013-10-30 152 63
    2013-10-31 157 63 13.25 0 1.58 0.00 1.58
    2013-11-01 162 64 13.25 3.5 1.58 0.29 1.87
    2013-11-02 167 65 13.25 3.5 1.58 0.29 1.87
    2013-11-03 173 65 15.9 0 1.89 0.00 1.89
    2013-11-04 179 67 15.9 7 1.89 0.59 2.48
    2013-11-05 185 67 15.9 0 1.89 0.00 1.89
    2013-11-06 187 69 5.3 7 0.63 0.59 1.22
    2013-11-07 195 69 21.2 0 2.52 0.00 2.52
    2013-11-08 203 70 21.2 3.5 2.52 0.29 2.81
    2013-11-09 212 71 23.85 3.5 2.84 0.29 3.13
    2013-11-10 219 72 18.55 3.5 2.21 0.29 2.50
    2013-11-11 224 73 13.25 3.5 1.58 0.29 1.87
    2013-11-12 232 73 21.2 0 2.52 0.00 2.52
    2013-11-13 237 74 13.25 3.5 1.58 0.29 1.87
    2013-11-14 242 75 13.25 3.5 1.58 0.29 1.87
    2013-11-15 247 75 13.25 0 1.58 0.00 1.58
    2013-11-16 251 76 10.6 3.5 1.26 0.29 1.55
    2013-11-17 255 77 10.6 3.5 1.26 0.29 1.55
    2013-11-18 261 77 15.9 0 1.89 0.00 1.89
    2013-11-19 271 79 26.5 7 3.15 0.59 3.74
    2013-11-20 279 80 21.2 3.5 2.52 0.29 2.81
    2013-11-21 288 80 23.85 0 2.84 0.00 2.84
    2013-11-22 300 81 31.8 3.5 3.78 0.29 4.07
    2013-11-23 308 83 21.2 7 2.52 0.59 3.11
    2013-11-24 313 84 13.25 3.5 1.58 0.29 1.87



    Sorry about format ..... any ideas on displaying a better format ?


  • Registered Users, Registered Users 2 Posts: 3 Throwaway Account


    May I ask who did you use as a supplier?