no life in the boiler...

  • 13-07-2010 9:29am
    #1
    Registered Users, Registered Users 2 Posts: 52 ✭✭


    Hi there lads,
    I have a recently renovated an old cottage but the boiler system was only changed about 10 years ago was getting very little use and was running fine up to recently. Not living in the house yet and i went to turn the heat on to get ready for a timber floor but when I switch on the heat the light on the switch is on but theres no life in the boiler. What does this usually mean? Thanks


Comments

  • Registered Users, Registered Users 2 Posts: 2,526 ✭✭✭JohnnieK


    Is it oil or gas?


  • Registered Users, Registered Users 2 Posts: 52 ✭✭supermilk1


    How ya johnnie,
    Its oil.


  • Registered Users, Registered Users 2 Posts: 138 ✭✭johnjoe 123


    1.....it could be airlocked as in no oil in tank if so get oil and bleeding srew bolt will be close to wer the flexable oil line enters the burner.2..... it could be on lockout if so theres a red light on the front of the burner press it and it should go. or 3....it could be the high limit stat if so theres 2 knobs on ur thermostat 1 4 controlling the temp the others a cover with a reset button under it screw off this knob/cap and reset trip...... if its none of the above youll need to explain more!!!


  • Registered Users, Registered Users 2 Posts: 44,080 ✭✭✭✭Micky Dolenz


    Just to add, ensure there is power going to boiler.

    If there is, if could be as johnjoe described. if you have power going through stat to burner, it is not the overheat stat. Check red reset light on burner.


  • Registered Users, Registered Users 2 Posts: 2,526 ✭✭✭JohnnieK


    As the lads said. Try those tests first.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 52 ✭✭supermilk1


    Thanks for the advice lads. tried ye're instructions but still no joy. it started up for about 10 seconds when i pressed the reset button but died after that. its a grant module 50 -70 if that helps.either way thanks again


  • Registered Users, Registered Users 2 Posts: 2,526 ✭✭✭JohnnieK


    Dose it actuaty fire for 10 seconds and then go out? did you vent the oil line?

    The fuel pump could be faulty or if it fires for a bit and goes out the photo cell could be dirty or faulty.

    I think you should call some one in to take a look.


  • Registered Users, Registered Users 2 Posts: 52 ✭✭supermilk1


    yes it starts for a few seconds before it dies.ya ill have to get someone in.im just gone out of my dept.please god it just needs to be cleaned. thanks for the help lads