Air Tightness Specialist

  • 27-05-2008 2:57pm
    #1
    Registered Users, Registered Users 2 Posts: 689 ✭✭✭


    Hi,

    Has anybody here contacted an Air Tightness Specialist for their build. i.e. somebody to recommend a product to achieve the required airtightness, instruction on installation and then commission/test the system once it has been istalled.

    Please give details if you have.

    Who?
    Costs?
    Masonry/Timberframe?
    Satisfied with service?

    Thanks.
    Mike.


Comments

  • Closed Accounts Posts: 495 ✭✭ardara1


    Mike2006 wrote: »
    Hi,

    Has anybody here contacted an Air Tightness Specialist for their build. i.e. somebody to recommend a product to achieve the required airtightness, instruction on installation and then commission/test the system once it has been istalled.

    Please give details if you have.

    Who?
    Costs?
    Masonry/Timberframe?
    Satisfied with service?

    Thanks.
    Mike.

    Hi Mike - air tightness in a build can not be bought - it's down to detailing.
    There is an assumed performance of 7 at Q50 when using the Accredited details asked for in the new Part L regulations that are coming into force in July -

    U-values of arounf 0.22 in the wall 0.20 in the floor etc (as muted in the new part L) require a better detailing regime - Enhanced Details (Again UK)
    using these assume an air permeability of 4 at @ Q50

    Below 4 - and there probably isn't enough natural ventilation for the occupant - then MV is probably required.


  • Registered Users, Registered Users 2 Posts: 2,292 ✭✭✭RKQ


    <snip>they supplied me and advised on installation. They arrange a "blow door test". I was happy with their service and products - Solitex etc.The tapes are great!


  • Registered Users, Registered Users 2 Posts: 46,547 ✭✭✭✭muffler


    RKQ wrote: »
    Try <SNIP>, they supplied me and advised on installation. They arrange a "blow door test". I was happy with their service and products <SNIP>etc.The tapes are great!
    PM the OP with the details please.