Wiring of Woodpecker boiler

  • 05-12-2006 6:13pm
    #1
    Registered Users, Registered Users 2 Posts: 164 ✭✭


    Hi all,

    There is a 4 wire cable out of the woodpecker boiler. An earth, neutral, and 2 more - a brown and a black. The manual only refers to a standard 3 wire supply.

    Is one a permanent live and the other a switched live?
    If so does anyone know which is which.

    I've email Gerkros, but no response as yet.

    Thanks in advance

    Pat


Comments

  • Registered Users, Registered Users 2 Posts: 68 ✭✭Copper


    Black is normally a permanent feed, brown switched. When the switched live is switched off, the permanent feed keeps the boiler running for a few seconds to stop pressure building up in it.

    You can always check the boiler manual or open up where the connections at the boiler are to be sure.