Changed the title of the thread.... You are free to discuss boiler operating....etc...

Enjoy.....

knighted_1 Banned
#47

gary71 said:
Correct burner pressure or correct co2 setting = correct gas rate, I use gas rating as proof of what I already know from testing it's a tool, not a necessitie,
nothing less than 19mbar at the appliance working pressure 1 mbar drop allowed, there is no problem getting the correct co2 at the correct working pressure and your on your own ajusting boilers in away not reconised by the manufactures ie. me, you reduce the gas to a low working pressure then any igniton issues you be fixing because I'll be looking for more gas before I get involved, Viessmann work at 11mbar working pressure allday everyday and that's the main boiler Martin has worked on the other is mine and I would be telling him the same thing, lastly no need to apolagise, gas fitting comes done to opinions and we all have one


you see this is the thing ,a gas rate is required by law now .if as suggested earlier that someone hangs a boiler and fires it up i gaurantee it will be overfiring if someone wants to post a boiler make and kw and the manufacturers stated m3ph i will do the calculation and show you how its overfiring -

gary71 "A Gasman"
#48

knighted_1 said:
you see this is the thing ,a gas rate is required by law now -
your right

knighted_1 said:
if as suggested earlier that someone hangs a boiler and fires it up i gaurantee it will be overfiring -

based on what studies, what are your gas qualification(apart from GID) and what have you studied to come to this opinion(apart from Mr Hogan).

slavetothegrind Registered User
#49

http://www.ferroli.co.uk/Product_Documentation/Domestic/Optimax_HE_18_S_Manual.pdf

in the case of the above boiler, you install it and check you have the required 20mb at the inlet. no further adjustment of gas pressure is allowed as the valve is sealed.
how do you propose to correct the overfire situation you believe to exist here?

me up for learning

1 person has thanked this post
Micky Dolenz Registered User
#50

slavetothegrind said:
http://www.ferroli.co.uk/Product_Documentation/Domestic/Optimax_HE_18_S_Manual.pdf

in the case of the above boiler, you install it and check you have the required 20mb at the inlet. no further adjustment of gas pressure is allowed as the valve is sealed.
how do you propose to correct the overfire situation you believe to exist here?

me up for learning



The baxi solo HE is the same, and there are a few others where there is no adjustment. If you find a problem with appliance firing etc when commissioning it, you would have to make a service call.

gary71 "A Gasman"
#51

Micky Dolenz said:
The baxi solo HE is the same, and there are a few others where there is no adjustment. If you find a problem with appliance firing etc when commissioning it, you would have to make a service call.


Don't go mixing up a real ignition or combustion issue with a made up over firing issue.

Micky Dolenz Registered User
#52

gary71 said:
Don't go mixing up a real ignition or combustion issue with a made up over firing issue.



I mean, if co2 readings are out or gas rate too high or low.

1 person has thanked this post
gary71 "A Gasman"
#53

Here are some facts:

1) The higher the C.V the more a supplier can charge(so ours is high because?)

2) A gas boiler shall be gas rated on commissioning.

3) you can only commission asper the manufactures instructions and none allow for the adjustment of the gas isolation valve

5) you can't adjust the gas rate on a condensing boiler other than the adjustment allowed by the manufactures on some gas valves to set correct co2. adjusting the gas inlet valve may put the working pressure at the appliance below the required amount specified in IS813 5.4.5.

6) The manufactures write different instructions for different countries so the values can change in the manuals although the boilers stay pretty much the same.

7) To date in this country no gas boiler made by my firm has had a issue with the high CV given by Bord Gais.

8) When designing and making appliances, manufactures use the European average calorific value which is 10.8 kWh/m3 as a starting point and not the UK CV value.

Joey the lips Stealing Hugs Chasing Kisses
#54

gary71 said:
Here are some facts:

1) The higher the C.V the more a supplier can charge(so ours is high because?)

2) A gas boiler shall be gas rated on commissioning.

3) you can only commission asper the manufactures instructions and none allow for the adjustment of the gas isolation valve

5) you can't adjust the gas rate on a condensing boiler other than the adjustment allowed by the manufactures on some gas valves to set correct co2. adjusting the gas inlet valve may put the working pressure at the appliance below the required amount specified in IS813 5.4.5.

6) The manufactures write different instructions for different countries so the values can change in the manuals although the boilers stay pretty much the same.

7) To date in this country no gas boiler made by my firm has had a issue with the high CV given by Bord Gais.

8) When designing and making appliances, manufactures use the European average calorific value which is 10.8 kWh/m3 and not the UK CV value.



This is why i orig closed the thread. No 3 was my understanding...

ps... you forgot 4.

gary71 "A Gasman"
#55

Joey the lips said:
This is why i orig closed the thread. No 3 was my understanding...

ps... you forgot 4.


Fact number 4) I'm sh1t with numbers

1 person has thanked this post
JohnnieK Registered User
#56

Joey the lips said:
Hi Folks...

Wondered if you can help. Was asked a question today i have not been asked in a while... Brother has a gas boiler thats 15 years old and sounds like its just about to set down...A couple of leaks...heatexchanger pump... etc...

Anyway traditionally what i would have done there is supply a boiler with a cast iron heat exchanger somethine like a suprima or a glowworm. You know why..the dirt etc...

Just wondering since condensing boilers have come in the standard seems to be aluminium heat exchangers which off course is prone to blocking...or are they...


The simple question i am asking is...what is now supplied for the retrofitting of a boiler...is it a condensing one with a fabricated heat exhanger and a serious system flush or is it something else...

Many thanks for parting with the knowledge....


A stainless steel heat exchanger is the only way to go Joey. The best corrosion resistance, and minimizes deposit build up due to having a smooth surface.

1 person has thanked this post
Joey the lips Stealing Hugs Chasing Kisses
#57

JohnnieK said:
A stainless steel heat exchanger is the only way to go Joey. The best corrosion resistance, and minimizes deposit build up due to having a smooth surface.


I like that but are they interchangable.. For example if i buy a make of boiler can i go off and buy a stainless steel heat exchanger.