How much power can be got from a socket?

  • 27-03-2014 2:25pm
    #1
    Registered Users Posts: 8,666 ✭✭✭


    Hi.

    How much power can be got from a socket? What would happen if it was overloaded?

    Example scenario:
    For testing things on my old PC, I connect a 20 inch CRT monitor + Desktop PC + Speakers to a single socket.

    Is this well within safety margins?

    Cheers.

    Mitch Hedberg: "Rice is great if you're really hungry and want to eat two thousand of something."

    Tagged:


«1

Comments

  • Registered Users Posts: 270 ✭✭liveandnetural


    BS1363-2:1995 requires for double socket outlets that both socket outlets have loads applied via test plugs, 1 test plug having a load of 14 amps whilst the other has a load of 6 amps, making a total load of 20 amps on the cable supplying the double socket outlet. The double socket outlet is then subjected to this loading for a minimum continuous period of 4 hours or longer until stability is reached with a maximum duration of 8 hours (stability being taken as less than 1 degC rise within 1 h). The test is passed if neither the terminals / terminations, nor the accessible external surface, increase in temperature by more than 52 degC.


    your safe enough with your pc stuff


  • Registered Users Posts: 8,666 ✭✭✭Worztron


    BS1363-2:1995 requires for double socket outlets that both socket outlets have loads applied via test plugs, 1 test plug having a load of 14 amps whilst the other has a load of 6 amps, making a total load of 20 amps on the cable supplying the double socket outlet. The double socket outlet is then subjected to this loading for a minimum continuous period of 4 hours or longer until stability is reached with a maximum duration of 8 hours (stability being taken as less than 1 degC rise within 1 h). The test is passed if neither the terminals / terminations, nor the accessible external surface, increase in temperature by more than 52 degC.


    your safe enough with your pc stuff

    Thanks for the explanation.

    Mitch Hedberg: "Rice is great if you're really hungry and want to eat two thousand of something."



  • Registered Users Posts: 1,890 ✭✭✭tomdempsey200


    I think the double sockets are rated up to 20amp total

    sockets and plugs give trouble with heavy sustained loads


  • Registered Users Posts: 936 ✭✭✭bassey


    Sockets on a 20A MCB/fuse so neglecting power factor you can draw 4.6 kW from the wall


  • Registered Users Posts: 2,637 ✭✭✭brightspark


    bassey wrote: »
    Sockets on a 20A MCB/fuse so neglecting power factor you can draw 4.6 kW from the wall

    its possible for the socket to be on a 32A MCB (ring circuit)


  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,532 Mod ✭✭✭✭2011


    Worztron wrote: »
    Hi.

    How much power can be got from a socket? What would happen if it was overloaded?

    Example scenario:
    For testing things on my old PC, I connect a 20 inch CRT monitor + Desktop PC + Speakers to a single socket.

    Is this well within safety margins?

    Work out the total load that you would like to draw from a single socket. Your example is likely to be a relatively small load, I would guess that it is under 6 amps, so well within safety margins.


  • Registered Users Posts: 1,890 ✭✭✭tomdempsey200


    its possible for the socket to be on a 32A MCB (ring circuit)

    the 'draw' is limited by the connected load

    or should be


  • Registered Users Posts: 2,637 ✭✭✭brightspark


    the 'draw' is limited by the connected load

    or should be

    Of course it is, the max continuous draw from a twin socket can only be 2x13Amps (assuming accurate fuses in plug tops.

    But the OP won't be be drawing anything near that with the load mentioned.


  • Registered Users Posts: 270 ✭✭liveandnetural


    Of course it is, the max continuous draw from a twin socket can only be 2x13Amps (assuming accurate fuses in plug tops.

    But the OP won't be be drawing anything near that with the load mentioned.

    according to mk its

    All MK socket-outlets are manufactured to comply with BS1363 part 2: 1995 and are rated at 13A per unit. Double socket-outlets have been manufactured and tested to exceed this rating by margin that allows electrical safety and reduces the risk of heat and mechanical damage to components due to overloading. It should be noted that BS1363 part 2: 1995 does not allow double sockets to operate at twice the permissible maximum loading and it should be remembered that double socket-outlets are not manufactured to be able to withstand a 26A load for sustained periods of time.

    Research by ourselves and third party organisations has shown that all MK double sockets can safely withstand a continuous load of 19.5A for an indefinite period. Increasing the load slightly will begin to cause heat and mechanical stresses on the components in a relatively short period. Testing showed that a load of 22.3A was sufficient to cause heat stress that would cause a browning of the faceplates and sufficient heat to cause insulation damage to cable cores. A load of 24A for 43 hours was sufficient to cause significant heat damage to the material in which the socket-outlet was situated and within 75 hours sufficient to cause significant damage that would lead to the very real potential of fire.

    MK recommend that users of their sockets consult professional design Engineers when designing installations to avoid the possibility of heat and mechanical stress to components and installations caused by overloading of MK socket-outlets.


  • Registered Users Posts: 2,637 ✭✭✭brightspark


    My initial post replying to Bassy, was to highlight that not all twin sockets are protected by a 20A MCB and that it was possible for a 32A MCB to be used. It is also likely that in an older installation the fuse (DZ2 type) might only be 16A on a radial circuit. (I think older ring circuits were protected by a 20A DZ2 fuse, but
    I'm not certain)

    But on a 32A ring circuit it is possible BUT NOT RECOMMENDED to plug in two 13A loads without tripping a circuit breaker! The total load then only being limited by the fuses in the plug tops.

    In an average house I would expect the only place where two large loads would normally be located close together is in a kitchen, where ring circuits are now prohibited.

    Perhaps the fact that a twin socket outlet is only able to safely supply a max current of ~20A, is reason why radial circuits protected by a 20A MCB should always be used in preference to ring circuits that are protected by a 32A MCB.

    And liveandneturals post would indicate that even 20A is slightly too high!


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal



    And liveandneturals post would indicate that even 20A is slightly too high!

    Dont forget the 20A MCB wont trip too quickly, if at all, with both sockets of a twin fully loaded to 13 amps each.


  • Registered Users Posts: 1,890 ✭✭✭tomdempsey200


    well that's it


    the OCPD is specifically designed to protect the final circuit cable not the accessory

    although afaik the accessories are usually closely matched anyhow


    the ring circuit is an anomaly anyhow in this regard and will prob eventually be eliminated altogether for domestic use


    it will still be useful for commercial and industrial though


  • Registered Users Posts: 270 ✭✭liveandnetural


    well that's it


    the OCPD is specifically designed to protect the final circuit cable not the accessory

    although afaik the accessories are usually closely matched anyhow


    the ring circuit is an anomaly anyhow in this regard and will prob eventually be eliminated altogether for domestic use


    it will still be useful for commercial and industrial though

    i would dissagree with this statment about ring circuits still very common to see them especially in large domestic instlations


  • Registered Users Posts: 1,890 ✭✭✭tomdempsey200


    i would dissagree with this statment about ring circuits still very common to see them especially in large domestic instlations

    yes that was their main use from my point of view
    a couple of rings circuits is a great job in addition to kitchen and utility radials

    do you not believe they will eventually be phased out of domestic use?

    unless they changed the rules that conductor size must match breaker size.. same as industrial ring ccts


  • Registered Users Posts: 375 ✭✭frankmul



    unless they changed the rules that conductor size must match breaker size.. same as industrial ring ccts
    I always thought that the cable was sized bearing in mind the mcb used?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,532 Mod ✭✭✭✭2011


    frankmul wrote: »
    I always thought that the cable was sized bearing in mind the mcb used?

    Calculate the design current, select a proactive device based on this, then select a cable that has a current carrying capacity that exceeds the rating of the protective device. Finish off by making sure that fault loop impedance and volt drop are not excessive and respecify the cable if required.


  • Registered Users Posts: 375 ✭✭frankmul


    2011 wrote: »
    Calculate the design current, select a proactive device based on this, then select a cable that has a current carrying capacity that exceeds the rating of the protective device. Finish off by making sure that fault loop impedance and volt drop are not excessive and respecify the cable if required.
    That's what I thought, I'm not sure what tomdempsey200 means


  • Registered Users Posts: 1,890 ✭✭✭tomdempsey200


    im saying that at the moment on domestic ring final circuits

    a 2.5mm conductor may be used on a ring circuit protected by a 32 amp mcb

    not a problem if the ring circuit stays intact


    im saying they may change the rules so that the current rating of the conductors forming the ring is greater than the mcb rating


    and they may not do this of course..


    they may do nothing..


    they may scrap the domestic ring circuit altogether..


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,532 Mod ✭✭✭✭2011


    im saying that at the moment on domestic ring final circuits

    a 2.5mm conductor may be used on a ring circuit protected by a 32 amp mcb

    not a problem if the ring circuit stays intact

    I am not a fan of ring socket circuits.
    However what you have is two x 2.5 T+E supplying the load, not one.
    So effectively a 5sq. conductor.
    im saying they may change the rules so that the current rating of the conductors forming the ring is greater than the mcb rating

    This is already the case. A "5 sq." can take in excess of 32A.


  • Registered Users Posts: 1,890 ✭✭✭tomdempsey200


    2011 wrote: »
    I am not a fan of ring socket circuits.
    However what you have is two x 2.5 T+E supplying the load, not one.
    So effectively a 5sq. conductor.



    This is already the case. A "5 sq." can take in excess of 32A.

    yes.. obviously if the ring circuit is intact

    but if not there's a potential for overload

    historically with 'domestic' there may not be competent people in charge of maintenance..to put it mildly

    and the rules can reflect this

    the circuit is idiot proofed by matching physical conductor size to mcb


  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,532 Mod ✭✭✭✭2011


    yes.. obviously if the ring circuit is intact

    Yes, it must be intact.
    but if not there's a potential for overload

    I don't know what you mean by this.
    Please explain.
    historically with 'domestic' there may not be competent people in charge of maintenance..to put it mildly

    and the rules can reflect this

    the circuit is idiot proofed by matching physical conductor size to mcb

    No regulations can prevent stupidity.


  • Registered Users Posts: 1,890 ✭✭✭tomdempsey200


    2011 wrote: »



    I don't know what you mean by this.
    Please explain.


    i will provide an answer to your question tomorrow

    if you don't figure it out in the interim


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,532 Mod ✭✭✭✭2011


    i will provide an answer to your question tomorrow

    if you don't figure it out in the interim

    The suspense is killing me, I won't be able to sleep :D:D

    Talk tomorrow.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    I don't know what you mean by this.
    Please explain.

    Im sure he means a 5 square conductor has potential to become a 2.5 conductor at any time, and could be loaded above 2.5 rating.

    Its a long time ago I said I am not a fan of ring circuits. They just dont seem like a proper electrical method, at least in my mad mind anyway.


  • Registered Users Posts: 1,890 ✭✭✭tomdempsey200


    Bruthal wrote: »
    Im sure he means a 5 square conductor has potential to become a 2.5 conductor at any time, and could be loaded above 2.5 rating.

    Its a long time ago I said I am not a fan of ring circuits. They just dont seem like a proper electrical method, at least in my mad mind anyway.

    i like them


    ring final( commercial and industrial) and ring mains

    but domestic ..maybe they'll make another change


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    i like them


    ring final( commercial and industrial) and ring mains

    but domestic ..maybe they'll make another change

    I never wired one in a house.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,532 Mod ✭✭✭✭2011


    Bruthal wrote: »
    Im sure he means a 5 square conductor has potential to become a 2.5 conductor at any time, and could be loaded above 2.5 rating.

    If the ring became 2 radials ?
    The same applies to any circuit fed by parallel conductors.

    I don't like them, either but when the ring is unbroken the cables are protected.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    2011 wrote: »
    If the ring became 2 radials ?
    The same applies to any circuit fed by parallel conductors.

    One of those newly formed radials could be supplying the entire load originally on the ring. Therefore, potential for overloading.


  • Registered Users Posts: 2,218 ✭✭✭deandean


    I run two, 3kw kettles from a twin MK socket the odd time and all is well. that's about 24A for a few minutes.


  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,532 Mod ✭✭✭✭2011


    Bruthal wrote: »
    One of those newly formed radials could be supplying the entire load originally on the ring. Therefore, potential for overloading.

    Potential alright, if there is a failure.
    Same with many circuits fed by parallel conductors, but I take your point.